Tapping off smoke alarm circuit allowed ?

Merry Christmas
Status
Not open for further replies.

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
110.8 Wiring Methods. Only wiring methods recognized
as suitable are included in this Code. The recognized methods
of wiring shall be permitted to be installed in any type
of building or occupancy, except as otherwise provided in
this Code.

I am unaware where 'tapping' into a interconnection of smoke detectors is ALLOWED.

I was unaware NM stopped being NM when installed between an arbitrary pair of appliances such as two smoke detectors.
 

John120/240

Senior Member
Location
Olathe, Kansas
Coordinate what? :blink:

When the smoke alarm sets, a signal voltage is sent down the red wire to the other smokes; can there be a possible short circuit if the smokes are on different phases?

pjholguin Coordinate What ? Make the circuit feeding the smokes a two wire (14-2 blk & wht) from the panel to the first detector. From first detector to 2nd, 3rd,..7th you would use a 14-3 blk & wht w/red for the interconnect. At a convenient spot say the 5th detector tap off for your Master Bed lights. Nowhere are we mixing phases.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
And to accommodate AC smokes with battery backup, the signal voltage on the red is almost certain to be a DC voltage with respect to the neutral. Which drives home the need to avoid crossing hot and neutral in any interconnection!
 
I understand how to wire the alarm circuit and my preference is to have only smoke/CO sensors on the circuit. The posts by mjf & buck don't sound like the alarms are the same circuits...that's how I read them.


pjholguin Coordinate What ? Make the circuit feeding the smokes a two wire (14-2 blk & wht) from the panel to the first detector. From first detector to 2nd, 3rd,..7th you would use a 14-3 blk & wht w/red for the interconnect. At a convenient spot say the 5th detector tap off for your Master Bed lights. Nowhere are we mixing phases.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I understand how to wire the alarm circuit and my preference is to have only smoke/CO sensors on the circuit. The posts by mjf & buck don't sound like the alarms are the same circuits...that's how I read them.
The smokes are all on the same circuit. Said circuit is allowed to have other outlets on it; in some areas it is required.
 
I understand how to wire the alarm circuit and my preference is to have only smoke/CO sensors on the circuit. The posts by mjf & buck don't sound like the alarms are the same circuits...that's how I read them.


Sorry if I was not clear.

All smokes on 1 circuit. Also on that circuit (tied in at any point) is at least 1 general use receptacle or lighting outlet.


I like to put a lighting outlet or 2 that the HO will notice quickly if not working.
 
Thank you. Wouldn't the HO noticed once he turned off the breaker for smokes when the started beeping... never mind...my bad! :slaphead:

Sorry if I was not clear.

All smokes on 1 circuit. Also on that circuit (tied in at any point) is at least 1 general use receptacle or lighting outlet.


I like to put a lighting outlet or 2 that the HO will notice quickly if not working.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
If one were to assume the red conductor is a class 2 conductor (which we really can't do without seeing a class 2 power supply to reidentify as class 1) then Goldigger was clarifying any Chapter 3 wiring method can be used; and it could be in the same cable as the 120v conductors supplying the smokes.

Of course, the fact that the instructions take it for granted that we're gonna use three conductor cable doesn't hurt. :)
 