hmmm, Φ=0, so if you size the gen in VA where load is 100Vacrms @ 100amps with no reactance, what size gen in VA do i build? hmmm, VA suddenly looks like kW.
you can twist the terms around all you want. kW and PF is just a twisting to make it easier for power folks to understand how much of their VA is not paid for by customer and how much overhead they need to account for. 100kW in yields 80kW paid for by cust, then the $kW cust better be larger than the $kW gen, otherwise might as well go back to basket weaving.
There is a key point here: kVA represents the generation capacity and the transmission capacity being used, but not the _power_ being generated.
The generator can only supply so much current. The transmission lines can only carry so much current.
With a unity power factor load, your 100kVA generator can supply 100kW. You probably need to dump 105kW of mechanical power into the generator to get this output.
With a 0.8 PF load, your 100kVA generator can only supply 80kW. You probably need to dump 85kW of mechanical power into the generator to get this output.
'Apparent power' is _not_ power, even though the units are the same. Apparent power is different from active power because it includes the transmission capacity being used for energy being shuttled back and forth.
Apparent power is a real concept, and is useful because it tells you how much of your capacity you are using, how much your wires will heat up, etc.