roger said:Rick, look at post # 11, this is simply a one line diagram and the grounded conductor is not shown.
Roger
You mean this?
Roger
480sparky said:Is this a more accurate drawing?
roger said:Now you have burned up the 120 volt load by supplying it with 240 volts.
Go back to the original illustration and think about it.
Roger
roger said:Yes.
Roger
480sparky said:There will be zero volts across the loads.
480sparky said:It won't work that way anyway.... they're on the same phase, so there's no voltage.
roger said:Draw it out with arrows for current flow, you will see a complete 40 amp circuit.
BTW, after the load we will definitely see zero volts.![]()
Roger
480sparky said:Where is it stated the load is 120v?
Look at the illustration. :roll:
You've overloaded the neutral, then.
roger said:Wrong.
Once again, your taking a simple one line diagram and not thinking it through, both sides of the circuit would be identical, i.e., they would both have a grounded conductor. (not a neutral)
Roger
480sparky said:And it would carry the sum of the amps coming from both breakers.
roger said:Yes it would.
Feeding two individual conductors with 20 amp breakers on the same leg or phase would achieve the same results.
Roger
RUWired said:of course this can't be a real situation because of field conditions and use. Having a disclaimer in the instructions to install on the same phase would'nt work unless the unit was rated for a maximum 240 volt
Think of taking a 40 amp single pole breaker and running two equal #12 conductors to a single 40 amp heating element, if you were to put an ammeter on the conductors one at a time they would be carrying 1/2 the load current which would be 20 amps.
Of course this is a violation of 240.8 in the real world.
Roger
480sparky said:But in order for current to flow, it would need the grounded conductor, so in effect you would have this:
Roger
roger said:Why? In this exercise the unit is is 120 volt and would fry on a higher voltage.
Roger
480sparky said:By what you're saying here, this is what you have:
No current can flow because there is no circuit.
RUWired said:That is my point about not being field friendly. Guy comes in and finds only two spaces open (pole position 1 and 3).Turns it on and smoke.Or am i missing the whole thing. He should be using a 40 amp single pole but only has two single 20's on the truck.
roger said:Why did you get rid of the grounded conductor? You have just lost all that you had learned.![]()
Roger
I know roger,i'm laughing at the whole sinerio.roger said:Rick, if the circuit is fed from the same leg or phase it will never be in jeopardy of a higher voltage.
Roger