roger said:Rick, look at post # 11, this is simply a one line diagram and the grounded conductor is not shown.
Roger
You mean this?
roger said:Rick, look at post # 11, this is simply a one line diagram and the grounded conductor is not shown.
Roger
480sparky said:Is this a more accurate drawing?
![]()
roger said:Now you have burned up the 120 volt load by supplying it with 240 volts.
Go back to the original illustration and think about it.
Roger
roger said:Yes.
Roger
480sparky said:There will be zero volts across the loads.
480sparky said:It won't work that way anyway.... they're on the same phase, so there's no voltage.
roger said:Draw it out with arrows for current flow, you will see a complete 40 amp circuit.
BTW, after the load we will definitely see zero volts.![]()
Roger
480sparky said:Where is it stated the load is 120v?
Look at the illustration. :roll:
You've overloaded the neutral, then.
roger said:Wrong.
Once again, your taking a simple one line diagram and not thinking it through, both sides of the circuit would be identical, i.e., they would both have a grounded conductor. (not a neutral)
Roger
480sparky said:And it would carry the sum of the amps coming from both breakers.
roger said:Yes it would.
Feeding two individual conductors with 20 amp breakers on the same leg or phase would achieve the same results.
Roger
RUWired said:of course this can't be a real situation because of field conditions and use. Having a disclaimer in the instructions to install on the same phase would'nt work unless the unit was rated for a maximum 240 volt
roger said:Yes it would.
Think of taking a 40 amp single pole breaker and running two equal #12 conductors to a single 40 amp heating element, if you were to put an ammeter on the conductors one at a time they would be carrying 1/2 the load current which would be 20 amps.
Feeding two individual conductors with 20 amp breakers on the same leg or phase would achieve the same results.
Of course this is a violation of 240.8 in the real world.
Roger
480sparky said:But in order for current to flow, it would need the grounded conductor, so in effect you would have this:
![]()
roger said:Yes it would.
Think of taking a 40 amp single pole breaker and running two equal #12 conductors to a single 40 amp heating element, if you were to put an ammeter on the conductors one at a time they would be carrying 1/2 the load current which would be 20 amps.
Feeding two individual conductors with 20 amp breakers on the same leg or phase would achieve the same results.
Of course this is a violation of 240.8 in the real world.
Roger
roger said:Why? In this exercise the unit is is 120 volt and would fry on a higher voltage.
Roger
480sparky said:By what you're saying here, this is what you have:
![]()
No current can flow because there is no circuit.
RUWired said:That is my point about not being field friendly. Guy comes in and finds only two spaces open (pole position 1 and 3).Turns it on and smoke.Or am i missing the whole thing. He should be using a 40 amp single pole but only has two single 20's on the truck.
roger said:Why did you get rid of the grounded conductor? You have just lost all that you had learned.![]()
Roger
I know roger,i'm laughing at the whole sinerio.roger said:Rick, if the circuit is fed from the same leg or phase it will never be in jeopardy of a higher voltage.
Roger