hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Dont follow. Neutral to bond are at service disconnects and 250.50 all grounding electrodes need to be bonded together in building. If GEC are installed per nec 2014 article 250.64(f)(3) with busbar in electric room outside of service equipment would that create objectionable current?two neutral to ground bonds on one electrical system(the same transformer)at two separated areas connected by conductive paths, i think this is your real problem.