Yes, I am.Anyone curious why this is so hard to explain to an apparent electrical contractor???
The thread has mentioned both 4/0 Al and 2/0 Cu, and has mentioned RHH-2 insulation. Presumably the 4/0 Al had RHH-2 insulation; has there been confirmation from the OP that the 2/0 Cu does as well? I think kwired was speculating that the 2/0 Cu may be THWN-2.The reason I told kwired to read post #48 is to clear up his understanding of what conductors are being used, it was stated clearly that they are RHH-2.
You need to go back and read all the way through it, it may help you understand why we are asking the questions we are asking. The OP has clarified what the conductors are just not what's happening between the LB and the panel. kwired stated he understood the conductors between the LB and the panel were THHN/THWN, post #48 (as well as few others) clears that up.The thread has mentioned both 4/0 Al and 2/0 Cu, and has mentioned RHH-2 insulation. Presumably the 4/0 Al had RHH-2 insulation; has there been confirmation from the OP that the 2/0 Cu does as well? I think kwired was speculating that the 2/0 Cu may be THWN-2.
Cheers, Wayne
I'm aware of the issues, MattG0311 first raised the likely problem in post #24, and in post #28 I quoted the language from OP's post #27 that seems to confirm that.You need to go back and read all the way through it
That's a 2017 reference. In the 2020 NEC it got promoted to 310.4(A).I'm not finding a table 310.104(A)
He said initially ran same RHW conductors between meter and panel. That did not pass inspection so he ran 2/0 copper, though did not specify what insulation type those were. Apparently still failed with same reasons. No we haven't gotten greatest confirmation of whether there is or isn't raceway all the way between meter and panel, but piecing things together seems there is only raceway from top of meter to the LB then just open conductor from there. OP keeps focusing on conductors being rated for crush resistance and "aerial use" but is misunderstanding what that might actually mean. The sections his inspector cited are correct. If he has SE cable between meter and socket that would be fine there but wouldn't be fine direct buried ahead of the meter - he has made it fairly clear he initially used same thing before and after the meter for conductors, it had RHW/RHH insulation on it and that did not pass. Seems very likely it was a triplex assembly and most likely also had a USE rating though he has never mentioned that.You need to go back and read all the way through it, it may help you understand why we are asking the questions we are asking. The OP has clarified what the conductors are just not what's happening between the LB and the panel. kwired stated he understood the conductors between the LB and the panel were THHN/THWN, post #48 (as well as few others) clears that up.
The company Solid Ground Construction is a GC but owns Forest City Electric LLC in Ohio. I have my doubts the question is being asked by the EC though.From the picture, I can almost guarantee there is no conduit between the LB and panel. I zoomed in on the pic and can see one hot leg and the neutral coming in a KO. Can't see where the other hot is, but bet it is also coming through a KO.
This is smelling like a GC not an EC is doing this work.