I understand and agree with the reasoning for that section that requires that, but think your example is a kind of side effect not taken into consideration when writing that section, yet they have had a chance to correct it but have not done so.Here's another one that takes the cake:
IF I have a branch circuit with #6 conductors on a 60 Amp breaker, then I need a #10 EGC.
Take that same circuit, but put it on a 20 Amp breaker, and now I need a #6 EGC??!?
Totally insane!!