I don't know why the inspector even mentioned it. He must have wanted to chit chat. Maybe lonely.Most of the ones we install are these combination types.
Before anyone points it out, ever since the inspector pointed this out, I never put the red conductor on the left side anymore.
I know it doesn't matter for single phase, but I want to develop good habits.
When they put the finish material, (stucco, brick, siding) on the outside, are you in violation by no longer having the 1/4" required air space for wet location enclosures and cabinets?Most of the ones we install are these combination types.
The cabinets have a 1/4" (reverse dimple) raised bump on the back. That takes care of the requirement.When they put the finish material, (stucco, brick, siding) on the outside, are you in violation by no longer having the 1/4" required air space for wet location enclosures and cabinets?
I think he means if you put the meter on the OSB sheathing, then stucco gets applied, covering the dimple and another ½" of the can.The cabinets have a 1/4" (reverse dimple) raised bump on the back. That takes care of the requirement.
Yes. That's exactly what I meant. If the stucco is applied to where it seals around the enclosures, have you lost your space for air movement or are the 1/4" dimples on the enclosures against the sheathing still considered as adequate for airspace?I think he means if you put the meter on the OSB sheathing, then stucco gets applied, covering the dimple and another ½" of the can.
I would say yes, you've lost your airspace. Whether it would get flagged is another story.Yes. That's exactly what I meant. If the stucco is applied to where it seals around the enclosures, have you lost your space for air movement or are the 1/4" dimples on the enclosures against the sheathing still considered as adequate for airspace?
Most of the house loads (laundry, added outside lights, the cameras) are presently on apt. 11's panel. I don't know the arrangement between the landlord and tenant.If this is an apartment building where is the service equipment for the apartments? Why is this service separate?
I concurI would say yes, you've lost your airspace. Whether it would get flagged is another story.
The stucco would be part of the wall, so for a metallic, surface-type enclosure, you'd need to maintain 1/4" between the stucco and the sides of the enclosure. The dimples take care of the 1/4" between the wall and the back of the enclosure, assuming the wall is flat there.Yes. That's exactly what I meant. If the stucco is applied to where it seals around the enclosures, have you lost your space for air movement or are the 1/4" dimples on the enclosures against the sheathing still considered as adequate for airspace?
I had a special solar rated combo that was made to be recessed. It had a flange all the way around, so half of the enclosure was recessed into the wall. So I don’t see any way it could have an air gap. I think the air gap requirement is to allow any moisture that gets behind the enclosure to evaporate, if it is sealed, no moisture can get back there.Yes. That's exactly what I meant. If the stucco is applied to where it seals around the enclosures, have you lost your space for air movement or are the 1/4" dimples on the enclosures against the sheathing still considered as adequate for airspace?
Then it's not a "surface-type enclosure," which is what the 312.2 requirement applies to.I had a special solar rated combo that was made to be recessed.
not a flush mount either.Then it's not a "surface-type enclosure," which is what the 312.2 requirement applies to.
Cheers, Wayne
Glue set up to quick.....I think it looks great, with one exception.
The lines on the male adapters don't line up.
Seriously, look nice.![]()