titan1021
Senior Member
- Location
- Northern California
I have been asked to install a receptacle for a large freight company in one of their distribution warehouses. The warehouse is 225'x 200' and of course they need a receptacle for a computer station on the complete opposite side of the warehouse from where the sub-panels are located.
I've got two options for routing the conduit and wiring to the desired location.
Option 1: Across the 30ft high steel truss ceiling creating a run of approx. 360' and a lot of extensive lift work.
Option 2: Utilizing an existing conduit that is run approx halfway to the desired location, by continuing the run along approx. 200' of a
conveyor belt system for a total run distance of approx. 460' (no overhead work required with this option)
When doing voltage drop calcs.
I come up with #4 for 360' at 120v 15amp (3% VD)
I come up with #3 for 460' at 120v 15amp (3% VD)
I looked into Buck Boost transformers but am not really familiar with them, I did see that they aren't recommended for vary load demands.
So am not sure the voltage coming from the transformer would be safe for the computers, should someone also plug another load in.
There is a 277v lighting panel that I can also access. Another option would be to run 277v to the location then step it down with a small transformer.
That calcs out at
#6 for 360' at 277v for 15amp (3% VD)
#6 for 460' at 277v for 15amp (3% VD)
Just hoping to get a little advice or input on which method would be the better way to go.
Thank you
I've got two options for routing the conduit and wiring to the desired location.
Option 1: Across the 30ft high steel truss ceiling creating a run of approx. 360' and a lot of extensive lift work.
Option 2: Utilizing an existing conduit that is run approx halfway to the desired location, by continuing the run along approx. 200' of a
conveyor belt system for a total run distance of approx. 460' (no overhead work required with this option)
When doing voltage drop calcs.
I come up with #4 for 360' at 120v 15amp (3% VD)
I come up with #3 for 460' at 120v 15amp (3% VD)
I looked into Buck Boost transformers but am not really familiar with them, I did see that they aren't recommended for vary load demands.
So am not sure the voltage coming from the transformer would be safe for the computers, should someone also plug another load in.
There is a 277v lighting panel that I can also access. Another option would be to run 277v to the location then step it down with a small transformer.
That calcs out at
#6 for 360' at 277v for 15amp (3% VD)
#6 for 460' at 277v for 15amp (3% VD)
Just hoping to get a little advice or input on which method would be the better way to go.
Thank you