Since UL 2331 used the term CCID (charge current interrupting device), that would be a "UL 2331 compliant default off CCID".
Thanks for the pointer to UL 2331. UL 2331-2 (Table 6) does specify the trip time allowed for a CCID5, and it matches the trip time allowed for a Class A GFCI under UL 943, (20/I)^1.43 seconds, with I in mA. So now the discussion is a whole lot less academic:
Under the 2020 NEC, there is no requirement for GFCIs to be listed. Per the definition in Article 100 (which just references trip time), a UL 943 Class A GFCI and a UL 2331-2 CCID5 are both "GFCI". So if we have an EVSE with CCID5, now the location of the outlet is determinative as to whether an outdoor hardwired installation at a dwelling unit complies with 210.8(F).
The 2023 NEC added the requirement to 210.8 that the GFCI be a "listed Class A GFCI". So for the outlet location to matter under the 2023 NEC, we'd need a CCID5 EVSE that also is listed under UL 943 to provide Class A GFCI.