Cable damage that merely exposes the conductors without severing them will pose a hazard that won’t be detected by the EVSE’s cable test.
Right, but we just extensively went over that the EVSE has an earth leakage/imbalance device
- Fault sensitivity of Min 15ma - Max 20ma trip for protection against electric shock of personnel. (NEC 625.22) (SAE J1772) (UL 2231)
- Retry charging up to 4 times after a 15 minute delay per event. (UL 2231)
It's the EVSE's job to monitor it's own freaking output cable. Putting an upstream GFCI on that is not helping the situation.
-
The NEC has muddied the waters. There was no need to mess with the global standards for this type of equipment. I'll do what I can to get the NEC to leave well enough alone for the next code cycle -- it may be an impossible tilting at windmills but I'll try. It's too important that these things work and not cut off in random ways that undermine people's transportation.
-
Imagine if the NEC required a gas vapor detection device on any gas fuel car with an electrical system, that then drained the gas tank if it semelled something. That's the kind of impact that turning off a charger has.
-
Note that UL 2231 retry requirement: that's sensible given the potential for water in the cable or ice or whatever. Give it a few cautious tries, and alert the owner on their cell phone if the vehicle can't charge. The EVSE is in a far better position to communicate the problem to the operator, compared to some pre-Internet dinosaur of a "listed" GFCI device.
-
That upstream GFCI trips and the EVSE can't even call home to complain. That's not the way to run a modern computer controlled smart device. The NEC committees don't seem to have seen this from a very modern lens yet.