A receptacle is not utilization equipment. Per the NEC it is a contact device.The word 'general' here is a red-herring you are throwing in. It is not used in any code definitions or requirements.
Both a GFCI receptacle and an EVSE are listed to a UL standard, yes. The particular standard they are listed to is not relevant to any code definitions or requirements we are discussing.
That does not settle whether the EVSE is part of the premises wiring or not. A service transfers energy between the utility and the premises and the service conductors and equipment are still part of the premises wiring. Very similar language in the definitions; Note that both actually say 'between', not 'from'. These definitions do not make the distinction you're claiming they make.
625.22 does not say 'before the EVSE'. Your statement completely misrepresents what that section says.
(A hardwired EVSE is not cord-and-plug connected, so the part where I truncated doesn't apply.)
In fact the language here is no different than the language in 210.8(A) through (C) and others. The "receptacle shall have" GFCI or the "equipment shall have" GFCI. This leaves the option open for the GFCI protection to be either upstream (e.g. GFCI breaker) or at the receptacle or equipment. There's no reference to the outlet and thus no need to look for the location of the outlet and decide which side of the outlet the protection has to be on. In neither case does it hinge on whether the equipment is part of the premises wiring system or where it is in relation to the outlet.
A GFCI also is not utilization equipment, its purpose is not to consume energy. It is a device for protecting personnel from ground faults. An argument can be made it is a controller of electrical current.
Yes, the NEC definition of equipment includes devices.
The NEC definition of utilization devices does not make any reference to it drawing current. Instead it mentions using electrical energy for purposes like heating, lighting, and electronic.
We do not consider all devices which have incidental current draw as utilization equipment, for example neither lighted wall switches nor occupancy sensors are included when making load calculations.
The NEC clearly requires GFCI protection to be before a plug and cord connected EVSE, so there is no reason to believe it considers EVSE protection to equal that of a GFCI.
Whether the NEC should be changed to remove GFCI protection requirements for some outlets such as hardwired equipment has not been part of my discussion.