A GFCI receptacle is part of a premises wiring system and is tested by UL for general connections using its 'contacts'.
The connection item shown in post #6, cannot be used on with any general device.
The word 'general' here is a red-herring you are throwing in. It is not used in any code definitions or requirements.
It is part of an assembly listed to UL, similar to the complete device shown in post #11.
Both a GFCI receptacle and an EVSE are listed to a UL standard, yes. The particular standard they are listed to is not relevant to any code definitions or requirements we are discussing.
The final assembly serves a single purpose of being part of an EV charging system. As shown in post #19, NEC 625 says the function of the EVSE is to transfer power from the premises wiring.
That does not settle whether the EVSE is part of the premises wiring or not. A service transfers energy between the utility and the premises and the service conductors and equipment are still part of the premises wiring. Very similar language in the definitions; Note that both actually say 'between', not 'from'. These definitions do not make the distinction you're claiming they make.
Specifically, 625.22 requires personnel, such as GFCI, protection to be located before (i.e. as part of the premises wiring) the EVSE, as evidenced by the requirement of GFCI at the plug end of a cord connected installation.
625.22 does
not say 'before the EVSE'. Your statement completely misrepresents what that section says.
625.22 Personnel Protection System: The equipment shall have a listed system of protection against shock of personnel. Where cord and plug connected equipment is used ...
(A hardwired EVSE is
not cord-and-plug connected, so the part where I truncated doesn't apply.)
In fact the language here is no different than the language in 210.8(A) through (C) and others. The "receptacle shall have" GFCI or the "equipment shall have" GFCI. This leaves the option open for the GFCI protection to be either upstream (e.g. GFCI breaker) or at the receptacle or equipment. There's no reference to the outlet and thus no need to look for the location of the outlet and decide which side of the outlet the protection has to be on. In neither case does it hinge on whether the equipment is part of the premises wiring system or where it is in relation to the outlet.
Let me acknowledge at this point that I've been playing devil's advocate. My position is that the a GFCI receptacle obviously can provide the protection required by 210.8(F). My reasoning is that the outlet is not a point in the strict mathematical sense, but is rather a location (albeit a fairly narrow one) that can encompass the device or equipment where current is 'taken' for the load. (See definition of outlet.) In my opinion one does not have to enage in the whole hairsplitting exercise of locating the 'outlet' to a set of terminals on a device or equipment, as ya'll have been doing.
But my point is that if one is going to be liberal in this regard when considering a GFCI receptacle - which is equipment, and a device, and also utilization equipment - to provide the outlet in 210.8(F) with the required protection, then one should be equally liberal in allowing a Level II EVSE to do so (assuming the EVSE has the required functionality, which is a separate issue). Both are the equipment at the outlet.
That said, I also think the trend of requiring "outlets" to have GFCI is a bad trend that is going to lead to further confusion and controversy of the kind we're witnessing here. It was started with 210.8(F) and now unfortunately has been expanded to change how 422.5 handles things, in a bad way that reduces options for manufacturers and installers. It doesn't appear to be being done in coordination with manufacturers or UL and I can ascertain for no good reason for it. It used to be clear that equipment "at the outlet" could provide the required protection (without having to ask whether it's part of the premises wiring or where exactly the outlet is). Now that's getting muddied.