• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

xmas lighting receptacles

Status
Not open for further replies.

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
It seems to me that the AHJ can decide if your "in the 2nd floor outside soffet " location is acceptable under the "or the like" definition of damp location in 408.6A. A 12 inch eave/soffit does not offer a lot of protection. I heard somewhere a local interpretation that defined the protection to be the area under the eave within a 45 degree angle of the roof edge. If I read this section correctly the AHJ could make you use an in-use cover unless it's an open porch area, mezzanine, or canopy.
It would probably help if we cited the entire sentence from 406.8 : A receptacle shall be considered to be in a location protected from weather where located under roofed porches, canopies, marquees,and the like, and will not be subject to a beating rain or water runoff. I would think the AHJ would have to take the section I hi-lighted under consideration before making a decision as to whether a receptacle should have a bubble cover or not.
 

w_d_anderson

Member
Location
Berlin, MA
The main point I was trying to make is that there is a very limited space under eaves which is not subject to beating rain. It is a judgment call. If you are recessing a box into the underside of the soffit I see no problem, damp location. As soon as you move down the wall with your outlet you move into a judgment call.
 

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
The main point I was trying to make is that there is a very limited space under eaves which is not subject to beating rain. It is a judgment call. If you are recessing a box into the underside of the soffit I see no problem, damp location. As soon as you move down the wall with your outlet you move into a judgment call.
I was assuming we were talking about mounting the receptacle in the soffet and not on the side of the house below the soffit. Sorry if I mis-understood.
 
Status
Not open for further replies.
Top