xmas lighting receptacles
cash
New member
I am installing receptacles in the 2nd floor outside soffet in my sisters house
for christmas lights. do i need to gfci them and have in use cover?
don_resqcapt19
Illinois
210.8(A)(3) requires GFCI protection and 406.8(B)(1) requires the in use cover if the receptacle is in a wet location. Your installation may be in a damp area and not a wet area and if so, it would require a cover that is weatherproof when the receptacle is not in use.
goldstar
New Jersey
BTW, I just found out about this recently but they are now making GFI receptacles rated specifically for outdoor use. They have a "w/p" stamped on the face. Has anyone heard of or have info on these ?
Howard Burger
Pierre, wouldn't one of those continuous use plastic or metal covers make the gfi weatherproof, or has that changed. 2nd Q: if the gfi is supposed to be a 'wp' gfi, do we still need a contiuous use cover or would a flap cover work? Thanks
Well, I just re-read 406.8 and it pretty much takes care of this question. Can't figure out how to delete the above so I guess I'll leave it.
Do weather-resistant recepts have some special code stamped on them to help me know which is which?
goldstar
New Jersey
tom baker
First Chief Moderator
Sure. Required in the 08 NEC, but the marking is WR for weather resistant. And its not just GFCI receptacles but any receptacle in 406.8
w_d_anderson
Berlin, MA
or the like
or the like
It seems to me that the AHJ can decide if your "in the 2nd floor outside soffet " location is acceptable under the "or the like" definition of damp location in 408.6A. A 12 inch eave/soffit does not offer a lot of protection. I heard somewhere a local interpretation that defined the protection to be the area under the eave within a 45 degree angle of the roof edge. If I read this section correctly the AHJ could make you use an in-use cover unless it's an open porch area, mezzanine, or canopy.
infinity
New Jersey
I don't see how the underside of a soffit can be classified as a wet location given the definition in Article 100 of Location, Wet.