Please help me settle a bet. Under the 2008 NEC, is a receptacle required where the red outlet is shown in this picture? It is a kitchen peninsula in a dwelling unit. The dark gray square is a sink.
Argument #1: Figure 210.52(C)(1) indicates that if the distance between the wall line and the back of the sink is less than 12", then the sink divides the countertop into a peninsula and an island. Therefore, a receptacle would be required where the red outlet is shown in the picture, to serve the "island" created by the sink's seperation.
If you subtract the overhang from the measurement from sink to edge of counter, you would have around 10" of depth of counterspace.
Argument #2: Figure 210.52(C)(1) does not apply to peninsula or island countertops, because the only code reference to Figure 210.52(C)(1) is in the text of 210.52(C)(1), hence the name of the figure.
210.52(C) states that where a sink is installed in a peninsula and the width of the countertop behind the sink is less than 12 in., the sink is considered to divide the countertop space into two separate countertop spaces. Since it asks us to measure the width of the countertop, the presence of an overhang has no bearing on whether we need a receptacle or not.
Since there is over 12" of space behind the sink, no separation is created, and one receptacle anywhere on the peninsula will suffice (provided there is not more than 6" of overhang in that location.)