Besoeker

Senior Member
Location
UK
One sue sign the transformer is not big enough is it won't allow the motor to run by dropping out contactors due to excessive voltage drop on starting. But OP has not reported any such happening. So reductio ad absurdum, the transformer is big enough.
An 875kVA transformer isn't big enough for a 1,000 hp motor. If you were in the business of designing drive systems you would have no difficulty in understanding that.
There is no ad absurdum about it.
 

Ingenieur

Senior Member
Location
Earth
An 875kVA transformer isn't big enough for a 1,000 hp motor. If you were in the business of designing drive systems you would have no difficulty in understanding that.
There is no ad absurdum about it.

let's agree to disagree
imho it is sufficient
especially if the 840 was measured at the drive output, then motor load is only ~750 kva (90 kva for the filter/xfmr consumption) on a 875 kva xfmr
need more info from the op
 

Ingenieur

Senior Member
Location
Earth
If it was, it wouldn't run over temp.

it did not run over temp
he said that is what he expected to see ('usually') but did not, but rather the output was clamped at 840 which surprised him (and imo impossible)
that is why we need more info
but on the surface, if measured at the drive out, the most convenient point, the xfmr only operated at 750 or 85%
 

Besoeker

Senior Member
Location
UK
Wouldn't it depend on how much the motor was loaded? Perhaps the motor was oversized, or the calculated size was just over the next size down?
Quite right. Possibly a number of things. But if the transformer got too hot that's one problem right there.
 

topgone

Senior Member
These things here got me confused. Why do other people here claim that the setup is okay when the OP mentioned "it failed"? Did I miss a lot?
 

Fulthrotl

~Autocorrect is My Worst Enema.~
An 875kVA transformer isn't big enough for a 1,000 hp motor. If you were in the business of designing drive systems you would have no difficulty in understanding that.
There is no ad absurdum about it.

1HP = 746 watts.
1,000 HP = 746,000 watts.

that's not allowing for any losses whatsoever.
no heat, transformer loss, zip.

125% would be 932,500 watts.
 

Ingenieur

Senior Member
Location
Earth
These things here got me confused. Why do other people here claim that the setup is okay when the OP mentioned "it failed"? Did I miss a lot?
failure not = burned up, damaged or over temp
he was told the output was clamped at 840 kva, not possible
it started and ran the motor fine
he did not know how they ascertained that
increase load gradually until output plateaued?
we do know where the 840 was measured, makes a big difference
filter takes 50-60 kva
xfmr consumes 40 or so
 

topgone

Senior Member
failure not = burned up, damaged or over temp
he was told the output was clamped at 840 kva, not possible
it started and ran the motor fine
he did not know how they ascertained that
increase load gradually until output plateaued?
we do know where the 840 was measured, makes a big difference
filter takes 50-60 kva
xfmr consumes 40 or so

For all you know, we have a similar setup that works fine in the plant. Our's is an 850kVA transformer driving a 665kW motor for a reciprocating pump! If you compare with the OP's setup, 875kVA for a 746kW (1,00hp) motor against our 850kVA for 665kW. The OPs setup is loading their transformer about 9.4 times greater than ours.
 
For all you know, we have a similar setup that works fine in the plant. Our's is an 850kVA transformer driving a 665kW motor for a reciprocating pump! If you compare with the OP's setup, 875kVA for a 746kW (1,00hp) motor against our 850kVA for 665kW. The OPs setup is loading their transformer about 9.4 times greater than ours.

I am having trouble with that math! Your transformer to motor ratio is only slightly higher than the OP (1.17 vs 1.28).

I dont think it ever went over temp. Here is what the OP said:

. I've never seen it before, usually it just runs over temp.

The way I read that, if you take into account the previous and next few sentences, he wasnt saying that his transformer went over temp. He was saying, in general overtemp is what he sees on an overloaded transformer versus the "current limit" phenomenon he thinks he is seeing now.
 

Besoeker

Senior Member
Location
UK
1HP = 746 watts.
1,000 HP = 746,000 watts.

that's not allowing for any losses whatsoever.
no heat, transformer loss, zip.

125% would be 932,500 watts.

Agreed. The transformer simply isn't big enough regardless of any other problems that there may be.
 

Sahib

Senior Member
Location
India
An 875kVA transformer isn't big enough for a 1,000 hp motor. If you were in the business of designing drive systems you would have no difficulty in understanding that.
There is no ad absurdum about it.
The OP question is 840KVA limitation of 875KVA transformer. My proof is no evidence other than OP statement existed for it.
 

Ingenieur

Senior Member
Location
Earth
For all you know, we have a similar setup that works fine in the plant. Our's is an 850kVA transformer driving a 665kW motor for a reciprocating pump! If you compare with the OP's setup, 875kVA for a 746kW (1,00hp) motor against our 850kVA for 665kW. The OPs setup is loading their transformer about 9.4 times greater than ours.

???
665/850 = 0.78
746/875 = 0.85
1.09 or 9% more
moot
when converted to kva for eff/pf for this motor range
BOTH are ok
 
Last edited:

Ingenieur

Senior Member
Location
Earth
1HP = 746 watts.
1,000 HP = 746,000 watts.

that's not allowing for any losses whatsoever.
no heat, transformer loss, zip.

125% would be 932,500 watts.

so?
the xfmr is rated in mva
the motor depending on measuring point
is between 740-840 kva both < 875
filter loss 60 kva
xfmr 40 kva
calcs http://forums.mikeholt.com/showthread.php?t=187812&page=5&p=1871852#post1871852

drive mfgs (link previously posted) state xfmr kva >= motor kva
which it is
and the filter reduces stress on the xfmr

no one can say the xfmr is too small
the data indicates otherwise
 

Ingenieur

Senior Member
Location
Earth
...
I dont think it ever went over temp. Here is what the OP said:

I've never seen it before, usually it just runs over temp.

The way I read that, if you take into account the previous and next few sentences, he wasnt saying that his transformer went over temp. He was saying, in general overtemp is what he sees on an overloaded transformer versus the "current limit" phenomenon he thinks he is seeing now.

I'm not the only one
imo it was NOT over temp
only output limited (impossible in this case)
 