This is from another site. No need to mention the poster. I think these two statements are a bit of a stretch but I may be wrong. What I do know is that if I can install a fixture directly to the box without the bar I always will.
If I have unused cable calmps in a box I will always remove them.
Any thoughts?
If I have unused cable calmps in a box I will always remove them.
Any thoughts?
The strap or the metal piece that comes with a light fixture must be used to install the fixture as outlined in 110.3(B).
If the box is shipped from the manufacturer with the clamps installed then the clamps can not be removed in the field. Even if they are removed they are still counted just as if they were there by the inspector or at least the ones I teach. I use the UL standard that the manufacturer is required to adhere to during the manufacture process for my reference in the class room. This would be UL Standard 514A as outlined in Index A of the NEC.