That 4" pancake has worked for me, but there is not enough room for in & out, you can only bring one 14/2 into the box (and that's only if your NM clamp is external).
And as long as the fixture is not a hanging type that has the conductors entering the box via an all thread tube, hickey, stud or what ever that is required by 314.16(B)(3) to be counted as a conductor making a 6 cu. in. box to small for a 14/2 with ground cable.