9-41 Log #3910 NEC-P09
Final Action: Reject
(314.16(B)(2))
_______________________________________________________________
Submitter:
Andrew Darois, David Kramer Electric
Recommendation:
Revise text as follows:
Clamps in molded plastic boxes that are built in shall not be counted.
Substantiation:
These boxes are made with the clamps. Their volume is
calculated taking into account the clamps. Some inspectors will have you count
the clamps.
Panel Meeting Action: Reject
Panel Statement:
The submitter?s substantiation is inaccurate. The total cubic
inches for nonmetallic boxes is determined with the internal cable clamps
removed prior to the determination by the third-party testing agency. The
requirement to take a single volume allowance for cable clamps is based on the fact that the clamps reduce the usable volume in the box when the box is wired.
A molded clamp will reduce the usable volume when it is employed.
Number Eligible to Vote: 12
Ballot Results:
Affirmative: 12
_______________________________________________________________