What is the word on using 14/2+G NM for switch legs?     Any trouble with remarking the white wire as far as the 2008 NEC goes?
We assume the fed is also 14/2. If the circuits is a 20 amp circuit then 14/2 would be a violation.What is the word on using 14/2+G NM for switch legs? Any trouble with remarking the white wire as far as the 2008 NEC goes?
Make sure that the remarked white is used as the supply to the switch and not the return to the lighting outlet.
It seems silly that we must recolor the wire so it's no longer white, but we must still use it as the white wire. :roll:Down on white, back on black. Remarking is required.
We assume the feed is on a 15 amp circuit. If the circuit is a 20 amp circuit then 14/2 would be a violation.
I agree either it's white or it's not. Which is it. If we re-color it, what difference does it make which leg it is. Just stupid. I'd much rather have the black feed the switch and recolor the white to red. Any electrician would make more sense of that.
Mark
If you think about it, most often with a 2-wire switch loop, the feed wire (white) is connected to one or more blacks, and that connection rarely needs to be disturbed in the future.I'd much rather have the black feed the switch and recolor the white to red. Any electrician would make more sense of that.
You'd be surprised. I once had an inexperienced helper who saw a white wire on a 3-way, and removed it from the terminal and connected it to the "other neutrals" in the box. :roll:Is there anyone who is qualified really going to pull out a switch, look at a black and a white wire hooked to it, and think, "Dang! This thing is going to create a dead short, what with putting the black and white together like that on a switch!"
Check out 200.7(C)(1).
Chris
In the sense that the white should only be used for the hot feed to the "farthest" 3-way, and the black and red as the travelers back, yes.Now does it apply to travellers also????
The white wire may be used as a traveler but not as a return to the light.Now does it apply to travellers also????
Chris
Yes but it isn't white if it is taped blacked.I think the idea behind this is not to have two white wires coming in to a light fixture