Riograndeelectric
- Lakewood Colorado
What that article within 422 is doing is granting permission to use a plug and cord connection. There are five requirements, one of which is the dedicated circuit. But the article is not requiring plug and cord connections. So we can infer that hard wiring is allowable. That will bring us to the question of which type of circuit can be used for the hard wire connection. I can only think of three rules that say that a particular type of circuit cannot have any other outlets. One is the SABC, and that is the one under discussion. (The other two are the bathroom receptacle circuit and the laundry circuit, but there may be others I have missed). My conclusion is that you can power the range hood via a hard wired connection on any circuit other than those three. I would be inclined to use the kitchen light circuit, since it is close by, and since it is likely to be lightly loaded.
Thank you Charle. I aprecciate your input as well as the froum members input
I would agree that the hood can be hard wired form any circuit other than the SABC,Bathroom, Laundry and possibly the furnace and or boiler circuit.