- Massachusetts
I only have to know that a grounding means exists.
That grounding means went away with the change of the rules.
It is really that simple.
Ah, but 406.4(D)(1) is saying where a "grounding means exists" and "grounding means" pre-dates the emergence of Grounding Conductor, Equipment.+1 "Grounding means" is simply a synonym for EGC. Wayne
As installed, the armored cable was a grounding means. That's a fact. As long as the armor is undisturbed, it is existing, and the Code grounding is preserved, in my opinion, unless the Code specifically reverses that as-installed-grounding.1918 NEC
When the service conduit is grounded, its ground conductor must be run direct from it to the ground connection. The interior conduit, armored cable or metal raceways, if well bonded to the service conduit, grounded as provided in this rule, need no additional connection.
The term EGC doesn't enter into it because it didn't exist before its 1968 NEC first writing. The cable armor of BX cable without a bonding strip is connected to ground when installed to 1918 NEC 15A i & n. (or subsequent Code editions, until BX is no longer manufactured.)Hi Al,
A couple questions for you based on your line of reasoning.
1) Under the current NEC, do you consider the cable armor of BX cable without a bonding strip to be an EGC? Or is it simply a grounding means that isn't an EGC?
In my opinion, 406(D)(1) never lets me get to 406(D)(2) because a grounding means exists, therefore a grounding-type receptacle must be installed.2) If the latter, how do you comply with 406(D)(2)?
I never am lead from 406.4(D)(1) to 250.118.3) If the former, how does it comply with 250.118?
I understand that is your opinion. . . and I have my opinion.That grounding means went away with the change of the rules.
Being non-compliant is not the same thing as being a hazard. But yes, the code change meant that millions of existing receptacle installations became non-compliant. That's OK until you replace the receptacle; then you have to make it compliant.If, in fact, your jump-to-250.118 opinion is accurate, then there is a whole lot of installed metal raceway (flex) with installed grounding-type receptacles in the millions, that are HAZARDS because they "have no ground" that are not being called out by the AHJs that I am experienced with.
2011 NEC said:406.4(D) Replacements. Replacement of receptacles shall comply with 406.4(D)(1) through (D)(6), as applicable
2011 NEC said:250.118 Types of Equipment Grounding Conductors. The equipment grounding conductor run with or enclosing the circuit conductors shall be one or more or a combination of the following:
If you're in for a penny, then you're in for a pound. If millions of grounding-type receptacles installed to the Code of their original install in a FMC (flexible metal conduit) system are RETROACTIVELY without an EGC, by your thinking, then you have, legally, an appearance safety with an existing grounding-type receptacle where there is no Code recognized connection to ground.Being non-compliant is not the same thing as being a hazard. But yes, the code change meant that millions of existing receptacle installations became non-compliant. That's OK until you replace the receptacle; then you have to make it compliant.
My apologies for not getting the question into my unedited initial previous post. This is VERY much about the Code.I thought you wanted to talk about the CODE, not how it is enforced. Apparently you have no solution to the difficulties I pointed out in your interpretation of 406.4(D) with respect to this no-longer compliant EGCs?
In my personal experience, as described in earlier posts in this thread, I find no Real World (in my Metro work area) parallel for the claims being laid out here. And to the contrary, my Real World experience with the AHJ of multiple jurisdictions has completely countered the Code interpretation you say is correct.What is the actual mechanism that RETROACTIVELY removes the legally installed state of a Code (of the date of it's inspection and approval) compliant installation?
The language "shall comply with 406.4(D)(1) through (D)(6), as applicable" means comply with any and all that are applicable. Do you disagree?Your point about the opening sentence of 406.4(D) doesn't say "ALL" applicable, only "as applicable".
Any time the NEC refers to an equipment grounding conductor, it means something that complies with 250.118. Do you disagree?it tells me, this rule, that the EXISTING grounding means is the "equipment grounding conductor" to be connected to.
Wayne, you are asking a question that I literally just answered.Any time the NEC refers to an equipment grounding conductor, it means something that complies with 250.118. Do you disagree?
It is my position that you have to SHOW ME in the language of the Code that is enforceable language that says the ONLY meaning of EGC, for ALL installations ever made and for new construction not yet installed, is in 250.118 (or equivalent) of the most current edition of the Code adopted into statute today. I am asking you to show me where the Code says legally installed grounding means that exists today as installed, is NOW NO LONGER a grounding means, and NEVER WAS a grounding means.Your point about the opening sentence of 406.4(D) doesn't say "ALL" applicable, only "as applicable". 406.4(D)(1) has an "or" before "equipment grounding conductor is (not was) installed", and does not have a test about the existing receptacle, so nongrounding or grounding-types existing has no bearing. The very next part is trump, do-not-pass-go, "grounding-type receptacles SHALL BE used". AND, it tells me, this rule, that the EXISTING grounding means is the "equipment grounding conductor" to be connected to.
You know, as I write that, I think to myself that this is where the Code allows that the existing grounding means exists as an equipment grounding conductor. . .
Wayne, in this thread, the question is about receptacle replacement to the grounding means of an existing wiring method (old non-bonding strip armored cable type BX). But since you seem to be tilting toward GFCI, AFCI, TR and WR requirements, then let's apply your Code logic:The language "shall comply with 406.4(D)(1) through (D)(6), as applicable" means comply with any and all that are applicable. Do you disagree?
Think about what you wrote, there. If, as you claim, the EXISTING inspected and approved (to the Code in effect at the time of approval) installations are "non-compliant" then, the existing installation is a LEGAL HAZARD to personnel for lack of GFCI, to property and people for lack of AFCI, to children for lack of TR, and to property and people for lack of WR.the code change meant that millions of existing receptacle installations became non-compliant. That's OK until you replace the receptacle; then you have to make it compliant.
The same thing occured with TR receptacles; millions of non-TR receptacles are now non-compliant, but they can stay until you replace them. At which point you have to replace them with a TR receptacle (for the code specified locations).
Maybe this thread should read >>
"Everything you'd ever want to know about BX, but were afraid to ask"
~RJ~
And as my questions suggest, your answer was unclear to me. So requoting what you see as an answer isn't as helpful as a simple yes or no. I still don't understand which of the following is your position:Wayne, you are asking a question that I literally just answered.
Since "grounding means" is undefined in the NEC, I obviously can't do that. However, I have demonstrated that BX cable armor without a bonding strip "IS NOT" and "NEVER WAS" an EGC.I am asking you to show me where the Code says legally installed grounding means that exists today as installed, is NOW NO LONGER a grounding means, and NEVER WAS a grounding means.
I'm making an analogy to other code sections, just as you brought up FMC in lengths longer than six feet.Wayne, in this thread, the question is about receptacle replacement to the grounding means of an existing wiring method (old non-bonding strip armored cable type BX). But since you seem to be tilting toward GFCI, AFCI, TR and WR requirements, then let's apply your Code logic:
Existing installations are rendered "no longer compliant" all the time by code changes. Absent an actual danger, there is no compunction to do anything to such installations. But if you modify them, your work is governed by the current code, so you basically have to bring anything you touch into compliance.Think about what you wrote, there. If, as you claim, the EXISTING inspected and approved (to the Code in effect at the time of approval) installations are "non-compliant" then, the existing installation is a LEGAL HAZARD to personnel for lack of GFCI, to property and people for lack of AFCI, to children for lack of TR, and to property and people for lack of WR.
"OK" is not defined in the NEC, so I can't show you that.And then, Wayne, you actually say "That's OK. . . " !!!!!!!! How is it OK, by Code language? Where does the 2014 NEC state that existing non-compliant to the 2014 NEC installation approved under earlier editions of the NEC are "OK"?
1) The 2014 term "EGC" includes BX armor without a bonding strip that was originally installed under a code permitting its use and since unmodified.
2) Such armor isn't a 2014 EGC, but it is a "grounding means".
3) Some other, subtly different position.
As I repeat: the problem with your approach is the assumption that 2014 NEC 250.118 establishes that an inspected and approved installation of a grounded system of armored cable type BX and associated fittings and boxes WAS NEVER a grounding means.406.4(D)(1) has an "or" before "equipment grounding conductor is (not was) installed", and does not have a test about the existing receptacle, so nongrounding or grounding-types existing has no bearing. The very next part . . . tells me . . . that the EXISTING grounding means is the "equipment grounding conductor" to be connected to.
. . . this is where the Code allows that the existing grounding means exists as an equipment grounding conductor. . .
I am familiar with local ordinance that is crafted to "maintain" the Premises Wiring (System) of occupancies within the local jurisdiction inspected and approved under earlier editions of the National Electrical Code. I have several examples of them in my Metro Area, and they are all subtly different from each other and NONE of them are in the National Electrical Code.But seriously, the NEC is typically adopted by a jurisdiction as the requirements for electrical work. Electrical work will legally require a permit and NEC compliance, but it is rare that a jurisdiction will legally require one to go back to prior legal work and update it to modern standards. [My city, Berkeley, does have such a requirement for certain seismic standards, such as unreinforced masonry and soft-story buildings.] So the result is that there are many existing, legal, non-compliant installations.
Yet it does apply when you choose to modify existing installations, and in several cases it gives you explicit allowances for existing installations that are not available in new installations. So when you choose to replace a grounding-type receptacle in an existing installation using unbonded BX cable armor as the grounding means, it prohibits you from using that unbonded BX cable armor as the EGC for a new grounding-type receptacle.But the reason there is a local ordinance to do so, helps to underscore that the NEC is a new construction standard that regulates new installation, and does not extend to the existing installation. The NEC has silences that are thunderous on this matter, in my opinion.