How would you go about correcting the 110.26(A)(1) violation created here when a mobile home was set by an existing service and the meter/panel is facing the wrong way? Well facing the wrong way when it's that close. You can barely open the panel and then it rubs the siding and you kind of have to force it open enough to get inside it.
I would like to just turn the meter/panel to the side along with riser and conductors. The bottom/feeder conduit goes to the other side where the former home was. It is useless and will have to be took out.