The following description is not the actual sequence of events. But it is the best way I can think of to describe the situation, without drawing a picture, which I cannot do, or taking a photo, and I have never been to this site.
Imagine a concrete wall that was supposed to be three inches thick. The electrical design shows some branch circuit panels surface-mounted onto this wall. All conduits (incoming power and branch circuits) will be entering from the top.
Now imagine that the concrete wall contractor made an error, and began to make the wall nine inches thick. The error was noticed when the wall was about 3 feet high. The rest of the wall, from that point to the ceiling, was built 3 inches thick. As you stand inside the room, and look at the wall, you see the wall coming up from the floor, then it recedes six inches, so that there is essentially a 6 inch lip (upon which you can set your coffee cup).
Question: Can you still mount panels on this wall, above the ?6 inch lip,? without having to use Unistrut to hold the panel away from the wall? 110.26(F)(1) says that the ?dedicated electrical space? extends from the floor. Well, if you mount the panel right up against the wall, then the space directly below the panel won?t extend to the floor. Rather, it will be blocked by the concrete wall.
Imagine a concrete wall that was supposed to be three inches thick. The electrical design shows some branch circuit panels surface-mounted onto this wall. All conduits (incoming power and branch circuits) will be entering from the top.
Now imagine that the concrete wall contractor made an error, and began to make the wall nine inches thick. The error was noticed when the wall was about 3 feet high. The rest of the wall, from that point to the ceiling, was built 3 inches thick. As you stand inside the room, and look at the wall, you see the wall coming up from the floor, then it recedes six inches, so that there is essentially a 6 inch lip (upon which you can set your coffee cup).
Question: Can you still mount panels on this wall, above the ?6 inch lip,? without having to use Unistrut to hold the panel away from the wall? 110.26(F)(1) says that the ?dedicated electrical space? extends from the floor. Well, if you mount the panel right up against the wall, then the space directly below the panel won?t extend to the floor. Rather, it will be blocked by the concrete wall.