14/4 w/ ground - NM cable
donf
I have a spec that calls for multiple installations of 3 way switches to conform with the 2011 NEC.
First, Virginia has not as yet adopted 2011. We are still on 2008 until the next release of the BC. I have gone through Lowes, HD, Grainger, Graybar without any joy.
Any ideas, short of conduit and 4 THHN individual wires.
raider1
Logan, Utah
I assume you are talking about the 2011 NEC requirement for neutrals to be brought to every switch location.
If you arrange your 3 way switches correctly you do not need 14/4 NM cable. Arrange your 3 way switches to avoid dead end 3 ways.
Chris
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
I agree with Chris-- Is there a special reason why you need 14/4 NM.
FYI- 14/4 or 14/2/2 generally is a special order in many areas.
mbrooke
Batteries Included
United States
Technician
I think it might have something to do with a neutral being required in newer code/local code or for electronic sensors if its a switch leg 3 way?
texie
Fort Collins, Colorado
Just feed one end of the 3 way, and take the load out of the other end... problem solved...
Exactly and as others said. Even before the new requirement for a neutral, as a rule, I always did it this way. Same for single switch points-I was never a fan of dead end (switch loops) switching. Maybe because I was heavily involved with lighting control at an early stage of the game. Of course there is the rare occasion where non dead ends are not practical and XX/4 cable would be handy.
donf
I know exactly that issue but that can be solved easily without 14/4.
Okay, have a "Spec" that is requiring the use of 14/4, per 2011 NEC. Even though we here in VA. are still using the 2008 edition.
I know how to wire the switch pair with 3 wire.
What I don't know is where to find 14/4. None of my local resources have it.
mwm1752
Aspen, Colo
I believe the cable is referred as 14-2-2 nm/ 12-2-2 nm capable of containing 2 - 120v circuits with their own grounded conductor for each circuit. What NEC article is it the spec requires 14-4nm? If it involves the grounded conductor then the spec for 14-4nm is not required when the same result can be achieved with 14-3 nm
Dennis Alwon
Chapel Hill, NC
14/4 is made as well as 14/2/2 -- they are different animals.
Dennis Alwon
Chapel Hill, NC
Southwire makes both 14/4-- Black/Red/Blue/White and 14/2/2 --Black/White and Red/ White with red tracer. Tell you suppliers to order it but I don't know why it is in the specs.
curt swartz
Electrical Contractor - San Jose, CA
San Jose, CA
Okay, have a "Spec" that is requiring the use of 14/4, per 2011 NEC. Even though we here in VA. are still using the 2008 edition. I know how to wire the switch pair with 3 wire. What I don't know is where to find 14/4. None of my local resources have it.
Who is specifying this? Someone with electrical knowledge or just some architect that knows the code requires a grounded conductor so threw that spec in? Is the spec actually telling you how to wire the 3-way switches including which switch the line and load connect? If you are not dead-ending the 3-ways what is the 4th wire supposed to be connected to? If you really need 4-wire cable any supply house can order it for you.