I hereby invoke "Charlie's Rule." :wink:IMO 210.52 specifically calls out that 210.52(1)-(4) are not covered by sections (A)-(H).
I hereby invoke "Charlie's Rule." :wink:IMO 210.52 specifically calls out that 210.52(1)-(4) are not covered by sections (A)-(H).
I hereby invoke "Charlie's Rule." :wink:Read it again, and you'll find that it doesn't say that. Rather, it says essentially that "these are in addition to those." IMO, both the "these" and the "those" are "covered" by the statement.
Sort of. But as I say earlier, I really look at it from the opposite direction. If you put a receptacle in a DR wall, then the circuit that feeds it will become, by definition, an SABC. So if you put a receptacle 7 feet above the DR floor, intending it to be dedicated to the plasma TV installed at that location, then (1) It can't be fed from a 15 amp circuit, and (2) That circuit can't also feed lights.So are you saying every receptacle outlet in kitchen, dinning room, etc needs to be on a SABC?
Sort of. But as I say earlier, I really look at it from the opposite direction. If you put a receptacle in a DR wall, then the circuit that feeds it will become, by definition, an SABC. So if you put a receptacle 7 feet above the DR floor, intending it to be dedicated to the plasma TV installed at that location, then (1) It can't be fed from a 15 amp circuit, and (2) That circuit can't also feed lights.
If I were ever to become a stickler for precision in the application of words (?Nay, never, not he,? they all cry in unison!), I might focus in on one particular word, emphasized below:What means this word, ?covered?? If I talk about something, then I will have covered the topic, right?
Suppose the NEC authors, in their infinite wisdom, enacted the following rule: ?All receptacles that are painted yellow must be installed horizontally. Exception: The requirement does not apply to receptacles that are painted yellow but that have alternating blue stripes.?
Clearly, this rule would ?cover? the yellow receptacles. But does it not also ?cover? receptacles that are yellow with blue stripes? The fact that the rule does not impose requirement on the yellow/blue receptacles does not change the fact that the yellow/blue ones are covered by the rule.
So now let us look at receptacles that are ?covered by 210.52(A).? To be specific, let?s talk about Bob?s receptacle under the DR table. 210.52(A)(3) says that you can?t count this one as being one of the required wall space receptacles. That covers the subject, doesn?t it. The receptacle under the table can?t replace one on the wall, but it is covered by the rule.
Conclusion: The receptacle under the table, being ?covered by 210.52(A),? goes on an SA circuit. QED.
the liscensed guy I worked with told me all dining rooms must be 12 wire, or 20 amps. I looked it up in the book, because that's what I like to do, and 210.52 B.1.? or so references if the room comes off the small appliance branch circuit it shall be 20 amp, but what if the room has a dedicated circuit? Thank you
See in this I disagree. To me covered is the application of the receptacles required in regards to the spacing and so on. I would venture to say it is like the issue of can you have a 15A receptacle in the bathroom if the minimum 20A receptacles and circuit is met buy 210.11[c][3]...sure we can have a 15A circuit in the bathroom supplying a receptacle as long as he circuit and receptacle required by 210.11[c][3] is met and all are on GFCI.
My belief is once the coverage to meet 210.52 are met, additional receptacles not required based on in this case the location would not be a covered receptacle.
I agree with this. But there is a major difference in the way the two articles, 210.11(C)(3) and 210.52(B)(1), are written. In the first case, the wording is in terms of, "at least one." In the second case, the wording is in terms of, "all.". . . we can have a 15A circuit in the bathroom supplying a receptacle as long as the circuit and receptacle required by 210.11[c][3] is met and all are on GFCI.
That is fine by me. Everyone is welcome to disagree with each other on this forum, so long as we keep it civil.. . . I just can't agree.
They are not players in this game. The opening line of 210.52 limits the discussion to 125 volt, 15 and 20 amp receptacles. But you knew that.What about 250v receptacles?
I may have to change my vote on that one.IMO it (is) not talking about . . . the items listed in (1)-(4).
That is fine by me. Everyone is welcome to disagree with each other on this forum, so long as we keep it civil.
They are not players in this game. The opening line of 210.52 limits the discussion to 125 volt, 15 and 20 amp receptacles. But you knew that.
I may have to change my vote on that one.Looking again at the wording of 210.52(B)(1), and re-invoking Charlie?s Rule, I see that the ?shall server all? part of the rule speaks only of 210.52(A), and not of 210.52 as a whole. The items (1) to (4) to which you refer come into the story before we get to 210.52(A). So perhaps they are not ?covered,? in the sense that I have been using that word, and they therefore are not required to follow the SABC rules. So go ahead, put that plasma TV receptacle 7 feet above the DR floor, put it on a 15 amp circuit, and connect the overhead light to the same circuit. I won?t mind.
I retire long before 2011 but they need to rewrite this in perhaps english
You know that this is the middle of 2009....right?
2011 is 18 months away. Hardly a long time, especially for old guys :grin:
So, Paul, would you also agree that a kitchen island could have one or more receptacles below the 1' line and/or beneath a greater-than-6" overhang, as long as at least one compliant receptacle was also installed? We had that debate in the past.When I think about covered I think about the specific spacing requirements covered by the section 210.52(A)-(H) directly. If a location is not addressed I tend to maintain it is not covered and I personally don't feel that receptacles installed not to meet any of the covered requirements of 210.52(A) and so on would actually be considered covered.
Both, really.lol....well are you trying to pull me into some debate their larry?...lol.....or do you really want my opinion...lol
I've never let that stop me.because I seem to be FULL of opinions people dont agree with these days...![]()