I work in an old steel mill in PA and most of our substations have ungrounded delta transformers. What brought me to this thread is that I'm trying to understand what is the code on EGCs for ungrounded delta systems? We bring 46kV into the plant and distribute 6.9kV around the plant to the substations mostly via underground PILC cable. When these lead cables blow and we replace them with dry cables, we're already usually over our conduit fills because the old lead cable is a much smaller diameter. Then til you add a ground wire, the conduits are really full. We've had contractors insist on pulling a ground wire with the current carrying conductors in the past because of 250.186. In order to get everything to fit in the existing underground conduits, we usually have to reduce the cable size. Fortunately we can get away with that in some places but in others, we need to maintain that capacity of the existing PILC cable. When I read 250.186 it says, where an ac system operating at over 1000 volts is grounded at any point, a grounded conductor shall be installed and routed with the ungrounded conductors to each service disconnecting means and shall be connected to each disconnecting means grounded conductor terminal or bus. But if the system is ungrounded (and there are equipment grounds present to grounding electrodes at each substation) is the EGC needed? What purpose does it serve other than bonding unitsub to unitsub? None of the old PILC cables have a ground wire pulled with them in the conduit. If anyone has run into this and can point me to a particular NEC article I would appreciate it.
250.4 the place to start and the wording generally reading 'equipment likely to become energized' and ' provide an effective fault clearing or fault carrying path'.
And this docoment for systems commonly installed that have been found to cause fatalaties, distributing power without also carrying an EGC or effective fault clearing path. This imo would be equally dangerous for grounded and ungrounded systems, but was common enough at one time. Called local peg grounding in the report, the remote equipment will float at the phase line voltage when it faults to ground.
Federal enforcement agency responsible for the health and safety of the nation's miners.
arlweb.msha.gov
First thing I would look at is the supply transformer nameplate for the secondary winding, it could be a Y secondary, even if all the loads are delta connected. And then the code references for it. A delta secondary winding could be grandfathered and compliant as a floating delta with conditions, but Y secondary could be a system required to be grounded. Over 1000 Volts systems usually have their own code references and I did not check them, just saying I would know where to start looking. You would first want to know if the secondary is delta or Y, and then if it is a system required to be grounded.
The loads are most likely delta, but that refers to the loads pre-semiconductor era, and again, MV stuff is different than 480. If it was a 480 secondary, following generations would have tried to add just about anything and everything to it, single phase lighting (with no neutral), drives, rectifier front end loads.
Any load on it with a rectifier front end, it's a good bet the load has some type of front end filter network that is Y connected and grounded. This would be a fault on a floating supply. Most floating three phase power, it's a good bet the first ground fault is already present.
Contiguous bonding of all metal and the contiguous EGC is absolutely necessary. With a grounded supply, the design intent is that the breaker will trip for a fault, and take the hazard offline. For a floating supply, everyone still thinks the same thing, that the breaker will trip. But the design intent is that the breaker will not trip. That's the problem with a floating supply, no one understands it. for a floating supply, the hazard remains on with power and no clue pretty much that any hazard exists. If you have a truly floating supply, you need a ghostbuster to go with it.
If you're here asking if you needs an EGC to distribute power around your plant, you should bring in a really good specialist to go over your system several times surveying, looking for the hazards, and then advising.
Your post is missing a lot of necessary information.