A way to intentionally get those voltages is to take ungrounded delta, connect three resistors in a wye configuration, two of them will be same resistance to get 137 volts across them and the other one with proper resistance to get 157 across it. Then ground the "wye point" that is not truly centered between all three corners of the delta supply.add the voltages he mentioned up, then divide by square root of three and you get ~248. Neutral point is not solid and has drifted from the true neutral point.
Add: maybe better wording would be grounded point has drifted away from the actual neutral point.
Whatever is going on in OP's situation is probably similar but maybe not intentional. Those voltages possibly change as loads change as well as it will shift "neutral" to a different position when the loads change.
Ground fault detection lights with one different lamp than the other two could easily do this also.