Yes, there would be no connection at the center point.Seems to me if two phase three wire were connected like shown there would be excessive current flow through the upper and left two coils, unless there is no physical connection at the center point, which it might be trying to show that I guess.
However, the common conductor in two phase three wire ( line C in post #55) will carry 1.414 times the current on lines A and B (assuming equal loads across A-C and B-C). So the common conductor would need to be sized proportionately larger than the other two.