Re: 6 disconnect rule violation?
The exception is for a sub panel feed by feeders and does not apply to this panel due to the fact that 225.36 requires to be rated as a service disconnect and not a sub panel.
Mike! The panel at the detached building is not a service! Look at the definition!
Service Equipment. The necessary equipment, usually consisting of a circuit breaker(s) or switch(es) and fuse(s) and their accessories, connected to the load end of service conductors to a building or other structure, or an otherwise designated area, and intended to constitute the main control and cutoff of the supply.
It has to be "suitable for service equipment." That does not make it service equipment. A pickup truck is suitable for hauling a piano. That does not make the pickup truck exclusively a piano hauler.
You're throwing yourself into a paradox of immeasureable scope - why would they go to all the trouble of writing the last half of 225 if it was already covered under the scope of 230?
How can we tell if a panel is rated as service equipment?
I don't know, but I will gamble that when the can is marked from the manufacturer as "Suitable For Use As Service Equipment", then we're on the right path.
230.71 which is the section that describes just what a service disconnect is also refers us to the requirements found in 408.36(A) where we are allowed no more than two mains for the service disconnect.
How do you get a main before the service disconnect?
Yada yada yada...
Would this not violate 408.36(A) in a service panel?
Yes, it would. I already said that, and admitted an error that I made when I was arguing with Kenny. I don't have time to look for it, it was just before you jumped back in on this. It's the post where I generated a one-line; one for a service, one for a detached building.
As long as you continue to confuse "disconnecting means" for "overcurrent protection" you will continue to misinterpret the sections related to this discussion.
I am not making this statement to undermine you. I am trying to get you to stop and
look for the difference. With this latest post, you have muddied so much material, it's staggering.
1. Consider that the term "disconnecting means" does not involve "overcurrent protection".
2. Then, consider why you believe (despite the laws of physics) that the OCPD at the originating structure does not protect the remote panel from damage from overcurrent.
3. Look at
225.40 Access to Overcurrent Protective Devices. Where a feeder overcurrent device is not readily accessible, branch-circuit overcurrent devices shall be installed on the load side, shall be mounted in a readily accessible location, and shall be of a lower ampere rating than the feeder overcurrent device.
Let me paraphrase:
Where the originating OCPD for the outside feeder is not readily accessible, you will install an OCPD on the load side of the feeder in a readily accessible location, and it shall be rated lower so that it kicks before the one in the house that is not readily accessible.
If we're required to install an OCPD at the end of that feeder anyway,
225.40 would be completely, utterly, miserably pointless.
225.40 is sitting here telling you that
otherwise an OCPD would not be required, Mike. Mull it over.
Take a deep breath.