Re: 6 disconnect rule violation?
By Marc: The rating of the breaker to the rating of the switch is a more accurate caparison.
How? A breaker is required to be sized to protect the conductors feeding a load and can be smaller than what it protects and still be safe.
A switch or disconnect on the other hand is rated for the load it will carry, and can't be smaller, but can be larger, and still be safe.
They are total opposite of one another?
Ok now for Mike:
The requirement for not more than two mains (disconnects) in a panel board can be found in 408.36 but I have already pointed this out.
It even goes so far as to say just how many single pole breakers (disconnects) that can be installed in it.
It does? Where does it say this in 408.36?
Remember a single disconnect can have multiple poles. And multiple single pole breakers with a handle tie is considered one disconnect. and a main breaker for a 120/240 volt service is a two-pole multiwire disconnect.
If you are installing a panel board in this remote building there is no escaping the requirements found in 408. The listing on a main lug panel will state that when it is used as service equipment it must conform with 408.
"when it is used as service equipment"
Yes it says that but in this garage it is not being "used as service equipment". If it was it would be fed by unprotected service entrance cables, the grounded conductor (neutral) will be bonded to the grounding conductor. (Main bonding screw installed).
This would not be allowed with a 4-wire feeder fed panel at a remote garage unless 230.40 exception #3 was used, or 250.32(B)(2) was used. the latter would still not cause it to be service equipment.
But in any case it will not be service equipment.
Here is why.
Look at the definition of service equipment in article 100:
Service Equipment. The necessary equipment, usually consisting of a circuit breaker(s) or switch(es) and fuse(s) and their accessories, connected to the load end of service conductors to a building or other structure , or an otherwise designated area, and intended to constitute the main control and cutoff of the supply.
They do not connect to the load end of service conductors, so it is not used as service equipment.
When we install a sub panel and we happen to use a main breaker panel and it even says "suitable for use as service equipment" is it a service panel? No. it's "suitable for use as service equipment" But that does not say it is service equipment, it only saying it can be used as service equipment if is connected to service conductors. If it is not connected to service conductors it is not service equipment. and the service equipment stops at the main service disconnect 230.1, so even a main panel in a dwelling is not service equipment if there is a disconnect ahead of it. That is fact.
Have you read 250.32 lately? I think you will find that a grounding electrode is required at the separate building just like at the service
The bonding of the grounded conductor (Neutral) to the grounding in the building has nothing to do with an electrode requirement.
It has to do with the bonding of the neutral conductor (grounded circuit conductor) to the grounding in the building, weather it be the EGC's or GEC or both. This is required at any service equipment that is used as service equipment, not at a sub panel!
I am opened minded to any explanation of what you think this means. Give it a shot and explain what suitable for service equipment means. Please insert code references.
I did see above.
as I have been putting in allot of overtime, since my vacation and shortage of good help put me behind.
I enjoy these little discussions as it keeps me looking.
And I did learn one thing I didn't know (most likely because I never read it this closely) is I never noticed that the handle ties was only allowed for multiwire circuits in 225.33(B) and in 230.71(B).
And that 225.33 spells out that it can not be more than six switches or six circuit breakers mounted in a single enclosure? I only saw the Six disconnects. which would explain 225.33(B) on the multiwire circuits?