Re: 6 disconnect rule violation?
OK,
Here is the photo in it's entirety:
The point of showing only half of the photo was to draw attention to the first part of the code requirement for the panel to NOT be used as a "lighting and appliance branch circuit panelboard". If this panel has the maximum of six disconnects as required and ONE of those disconnects supplies a lighting or appliance branch circuit then it has violated the code of "more than 10%" and therefore no longer qualifies as "suitable for use as service equipment".
This also has nothing to do with how a panel qualifies as "suitable as service equipment" or if it has a green screw in the first place.
Read the code sections without prejudice and see what conclusion you reach.
OK,
Here is the photo in it's entirety:
The point of showing only half of the photo was to draw attention to the first part of the code requirement for the panel to NOT be used as a "lighting and appliance branch circuit panelboard". If this panel has the maximum of six disconnects as required and ONE of those disconnects supplies a lighting or appliance branch circuit then it has violated the code of "more than 10%" and therefore no longer qualifies as "suitable for use as service equipment".