Now, one thing I will agree with is the benefit of insulation testing at the completion of a job. We do that often as it is a called for in many of our job specification.
I?m giving up, I?m right in that everything should be tested and recorded and you?re right because there are more of you.
Now if someone comes up with a logical explanation of why things shouldn?t be tested other than MCB?s I?ll listen.
I think I?d rather be certain that a device will operate within its set parameters than rely on what it says on the box.
Regarding my statement about the RCD exploding, a 125A RCD is a bit unforgiving with an internal short circuit.
OK, why is it that previously in this thread I was told how much simpler an RCD was than a GFCI?
An RCD is simpler because it contains no electronics: (see attached pictures)
A toroid + solenoid is a lot less likely to fail, nuisance trip or do this:
http://forums.mikeholt.com/attachment.php?attachmentid=750&stc=1&d=1188559293
http://ecmweb.com/site-files/ecmweb.com/files/archive/ecmweb.com/mag/903ecmFORENpic2.jpg
The only seem complex to you because in some other parts of the world GFCIs/RCD/GFPs ect must all undergo testing to produce trip data regardless of their internal design. If a US GFCI was shipped and used in the UK it to would have to under go elaborate testing under UK regs.
What 'wear' the parts are stationary other than a trip. If anything they might stick due to non-use but that is a problem every molded case circuit breaker has and we don't test them either. They are far to inexpensive to bother doing load testing of them. If they are suspect they are simply tossed out.
These trip mechanisms can seize from foreign infiltration like bugs, water ect. Any grease can dry out inside. I have pushed test buttons on outdoor GFCIs that would not even move. Even if the mechanical parts are ok, their is a printed circuit board that can act up.
The mechanical parts are the same as our standard thermo-magnetic trip breakers. There is no wear unless they happen to be tripping all the time and my experience tells me that wear makes them subject to early triping not late.
Depends. For a GFCI breaker yes, for a GFCI outlet, that could be debated.
If the resister burns out the test button would not trip it so it would not pass the test. In other words .... no danger.
And if the test button isn't working then the RCD would immediately be labelled defective without further testing.
Call me very doubtful.
We know!
I am sorry you cant understand it but that does not change the fact it is enough.
From a North American document stand point you are correct, it is enough. From a UK regulation standpoint its not.
Im sure in reality the test button is sufficient in most cases, but why not rest assured for those cases where something might fly under?
I know you will think this is also over the top, but in the UK all completed installations must undergo an "earth fault loop impedance test" which in a nut shell must show the EGC is intact (not broken).
Might be excessive, but in the rare event an open ground exists (a life safety hazard) why not find out before something goes horribly wrong?
No need for that information, it only makes pretty reports.
I like pretty
One the breaker leaves the factory the trip time and trip level is not going to drift unless the mechanical parts seize up ....... and they it wont test with the button.
Any documents supporting that statement, or that the circuit board/ mechanical trip behavior will never change?
Now, one thing I will agree with is the benefit of insulation testing at the completion of a job. We do that often as it is a called for in many of our job specification.
If it is within the standard, do we really care about the exact numbers? I expect that the GFCI standard specifies the resistance of the resistor or the amount of current that it should flow at 120 volts. I don't have a copy of the standard to verify that. Most GFCIs trip much quicker than what the standard permits. I think if there was any delay, even a delay much less than the 3.7 seconds that the standard permits, I would replace the device.
These worthless devices were forced down our throats by overzealous jackasses who call themselves code authorities, who never met a rule they didn't like. They have long refused to address the issue that inferior wiring methods (chiefly backstabbing) have caused most of the problems the devices were supposed to "fix". I have replaced dozens of backstabbed devices that were "protected" by AFCI breakers that never tripped.
I have been fortunate to see only a few afci's nuisance tripping but am still angry at how much business has been lost because of the increased costs brought on by these devices.
Code authorities, open wide so we can shove them back down YOUR throats. Manufacturers, who probably bribed the authorities, you get in line too.
An RCD is simpler because it contains no electronics: (see attached pictures)
A toroid + solenoid is a lot less likely to fail, nuisance trip or do this:
http://forums.mikeholt.com/attachment.php?attachmentid=750&stc=1&d=1188559293
http://ecmweb.com/site-files/ecmweb.com/files/archive/ecmweb.com/mag/903ecmFORENpic2.jpg
The only seem complex to you because in some other parts of the world GFCIs/RCD/GFPs ect must all undergo testing to produce trip data regardless of their internal design. If a US GFCI was shipped and used in the UK it to would have to under go elaborate testing under UK regs.
These trip mechanisms can seize from foreign infiltration like bugs, water ect. Any grease can dry out inside. I have pushed test buttons on outdoor GFCIs that would not even move. Even if the mechanical parts are ok, their is a printed circuit board that can act up.
Depends. For a GFCI breaker yes, for a GFCI outlet, that could be debated.
And if the test button isn't working then the RCD would immediately be labelled defective without further testing.
From a North American document stand point you are correct, it is enough. From a UK regulation standpoint its not.
Im sure in reality the test button is sufficient in most cases, but why not rest assured for those cases where something might fly under?
I know you will think this is also over the top, but in the UK all completed installations must undergo an "earth fault loop impedance test" which in a nut shell must show the EGC is intact (not broken).
Might be excessive, but in the rare event an open ground exists (a life safety hazard) why not find out before something goes horribly wrong?
I like pretty
Any documents supporting that statement, or that the circuit board/ mechanical trip behavior will never change?
Electrical/Electronic Technical Note 91-1
December 18, 1991
How to Test the Operation of a GFCI
The Office of Electrical, Electronic, and Mechanical Engineering Safety Standards does not recommend the use of GFCI testers as a means of determining compliance with ?1926.404(b)(1)(ii), as such testers may not produce accurate results. Ground-fault circuit interrupters incorporate a testing circuit that can be used to determine whether or not the device itself will function as intended. No further tests are necessary.
Any GFCI tester that puts a resistive load between the ungrounded circuit conductor and the equipment grounding conductor1 to measure the current at which the device trips is subject to errors due to voltage fluctuations. If the circuit voltage is 100 volts, the tester could indicate that a GFCI tripped at 7.2 mA when it would actually have tripped at 6.0 mA. (See attachment.)
Testers like the Greenlee model 5708,(2) described in Mr. Loebach's memorandum (attached), cannot produce a reliable indication of the trip level of a GFCI. This device sends a 200-millisecond pulse through the grounding conductor at various current levels. A GFCI may not trip at minimum current levels (that is, 6-20mA) in such a short period of time. (For example, UL Standard 943 allows trip times of up to 1.5 seconds at 15mA.) This tester provides a 4-second interval between pulses and cannot be adjusted to provide a longer pulse or a shorter interval.
Additionally, an employer cannot reasonably be expected to know at what level his or her GFCIs trip. A reasonable person would only expect the employer to check them periodically using their built-in test mechanisms. Assuming that test equipment could accurately detect a GFCI that trips at too high a current, the employer should not be penalized for conditions beyond his or her normal control.
__________________________
(1) Deliberately putting current through the equipment grounding conductor is undesirable and, under certain conditions (for example, in a hazardous location), is unsafe.
(2) This device is not currently approved by a nationally recognized testing laboratory and does not meet OSHA's electrical safety standards. Therefore, it should not be used by OSHA compliance staff.
A citation in such cases may be warranted -- penalties are not.
The supervisory circuit built into a ground-fault circuit interrupter is designed to cause tripping even when the circuit voltage is 85 percent of rated voltage (102V for a 120-volt device). At rated voltage, the current employed by the supervisory circuit may not exceed 9mA. Thus, it gives an indication of the operability of the GFCI at currents approaching the trip level. It may not give an indication of whether the GFCI actually opens the circuit; however, this can easily be determined by plugging utilization equipment into the circuit in question.
For these reasons, the Office of Electrical, Electronic, and Mechanical Engineering Safety Standards recommends that the compliance staff use the test button on a GFCI in combination with an attached load plugged into the circuit to be tested rather than a GFCI tester. A plug-in ground continuity tester would suffice as an attached load. If the lights on the continuity tester go out when the test button is pressed, the GFCI can be assumed to be operating correctly. If the lights stay on or if the test mechanism fails to operate, the GFCI is faulty, and a citation would be warranted.
UL GFCI Tests
Every GFCI must pass the following end-of-line manufacturing tests:
1.no trip below 4mA (no load)
2.must trip at 6mA (no load)
3.no trip below 4mA (with load) at rated voltage
4.must trip at 6mA (with load) at rated voltage
5.must trip with 2 ohm grounded neutral
6.must trip within 25 ms with a 500 ohm fault
7.must trip with test button at +10/-15% rated voltage
8.must not trip with noise test of GFCI Standard
9.calibration test at +10/-15% rated voltage
GFCI Testers
Why are testers used?
?verify operation of the GFCI
?check protection of downstream receptacles
Will not test:
?GFCI calibration
?ALL types of improper installation
?Danger on 2-wire circuits
Will test for some types of improper installation:
?line/load reversal
?which outlets are protected by GFCI
?reverse polarity
?presence of the equipment ground
Benefits of UL943 (GFCI) vs. IEC (RCD)
Increased Safety Benefits
UL943 Max 6 mA - threshold for ?let-go? current.
IEC Min 20 mA - threshold current for ventricular fibrillation.
Receptacle End of Life indication
Grounded Neutral protection
Portable units - Load protection if both supply neutral and ground conductors are open together.
Hold on there partner.
I don't know anything about RCDs, I have never claimed they are complex or basic. I was pointing out that you and Tony S are saying entirely different things about them.
You have said they are simpler than GFCIs. Tony says they are more complicated than GFCIs.
So in other words it did not pass the test.
Seems like the test button did its job.
No debate, the 'wear parts' of a GFCI outlet are not the parts that have anything at all to do with the trip characteristics.
I work and live in North America, this forum is primarily North American. My comments are all based on that fact.
I am not trying to change what other areas do or require.
Because the idea is practical safeguarding not absoulutly safeguarding. The cost to benefit has to be there.
I have not seen you post any links or info showing that things are 'flying under' that seems to be an assumption you are making.
Actually I do not think that would be over the top at the time of completion. I take grounding pretty seriously.
Over the top would be requiring that same test on a annual basis.
I agree, one of the things I work on often is parking lot lighting and I honestly worry about the condition of the EGC. Often these circuits operate at 277 volts to ground and it is not that unusual for a hot conductor in the pole to short to to the pole due to movement from wind and time. If the EGC is not intact they pole will be live. That scares me, I never want to hear someone was hurt or killed by a pole I was the last to work on.
Great, test all you want just don't try to push it on the rest of us as a regulation.
I am claiming that the electronic parts will either work or not and that their time / current levels will not change over time.
I have not claimed the mechanical trip parts will not wear out or gum up. However the trip button will determine if the parts are gummed up. If the parts were out my experience tells me the breaker is gets easier to trip.
All the mechanicals inside the GFCI breaker are the same as in a standard molded case breaker. Do you think standard molded case breakers should be load bank tested?
How about you posting some legitimate evidence or statistics that shows the test button does not do the job?
A little reading for you.
https://www.osha.gov/pls/oshaweb/owadisp.show_document?p_table=INTERPRETATIONS&p_id=20553
Electrical/Electronic Technical Note 91-1
December 18, 1991
How to Test the Operation of a GFCI
The Office of Electrical, Electronic, and Mechanical Engineering Safety Standards does not recommend the use of GFCI testers as a means of determining compliance with ?1926.404(b)(1)(ii), as such testers may not produce accurate results. Ground-fault circuit interrupters incorporate a testing circuit that can be used to determine whether or not the device itself will function as intended.
No further tests are necessary.
Any GFCI tester that puts a resistive load between the ungrounded circuit conductor and the equipment grounding conductor1 to measure the current at which the device trips is subject to errors due to voltage fluctuations. If the circuit voltage is 100 volts, the tester could indicate that a GFCI tripped at 7.2 mA when it would actually have tripped at 6.0 mA. (See attachment.)
Testers like the Greenlee model 5708,(2) described in Mr. Loebach's memorandum (attached), cannot produce a reliable indication of the trip level of a GFCI. This device sends a 200-millisecond pulse through the grounding conductor at various current levels. A GFCI may not trip at minimum current levels (that is, 6-20mA) in such a short period of time. (For example, UL Standard 943 allows trip times of up to 1.5 seconds at 15mA.) This tester provides a 4-second interval between pulses and cannot be adjusted to provide a longer pulse or a shorter interval.
Additionally, an employer cannot reasonably be expected to know at what level his or her GFCIs trip. A reasonable person would only expect the employer to check them periodically using their built-in test mechanisms. Assuming that test equipment could accurately detect a GFCI that trips at too high a current, the employer should not be penalized for conditions beyond his or her normal control.
(1) Deliberately putting current through the equipment grounding conductor is undesirable and, under certain conditions (for example, in a hazardous location), is unsafe.
(2) This device is not currently approved by a nationally recognized testing laboratory and does not meet OSHA's electrical safety standards. Therefore, it should not be used by OSHA compliance staff.
A citation in such cases may be warranted -- penalties are not.
The supervisory circuit built into a ground-fault circuit interrupter is designed to cause tripping even when the circuit voltage is 85 percent of rated voltage (102V for a 120-volt device). At rated voltage, the current employed by the supervisory circuit may not exceed 9mA. Thus, it gives an indication of the operability of the GFCI at currents approaching the trip level.
It may not give an indication of whether the GFCI actually opens the circuit; however, this can easily be determined by plugging utilization equipment into the circuit in question.
For these reasons, the Office of Electrical, Electronic, and Mechanical Engineering Safety Standards recommends that the compliance staff use the test button on a GFCI in combination with an attached load plugged into the circuit to be tested rather than a GFCI tester. A plug-in ground continuity tester would suffice as an attached load. If the lights on the continuity tester go out when the test button is pressed, the GFCI can be assumed to be operating correctly. If the lights stay on or if the test mechanism fails to operate, the GFCI is faulty, and a citation would be warranted.
Agreed.......so why not those who have that GREATER knowledge continue to press for change if they believe it is so. Let's face it...the Home Builders Association has the deepest pockets of all of the anti-AFCI proponents and pay for many independent studies and they serve on CMP 2......yet again they FIGHT the AFCI at every chance so why would they have not proposed data on contrary to what the manufacturers claim. Let's not say it is because they are in the pockets of the manufacturers because I know that not be true having worked with both......so.....so much theory....
So with all the passion to debunk AFCI's.....why would someone not put together the data to prove them wrong and take all the glory for saving mankind from needless wasted spending......WHY?
I don't think Tony ever explicitly said they are more complex.
Your GFCI is identical to a 3 pole RCD baring the leakage current rating.
The sad part is US GFCI are full of electronics, where UK RCDs are just a toroid coil and a solenoid?
Benefits of UL943 (GFCI) vs. IEC (RCD)
Increased Safety Benefits
UL943 Max 6 mA - threshold for ?let-go? current.
IEC Min 20 mA - threshold current for ventricular fibrillation.
Receptacle End of Life indication
Portable units - Load protection if both supply neutral and ground conductors are open together.
True, because the resistor inside could pass 500ma. Its not known.
Via set standards, of course. At one time seatbelts were not required for Cars.
This actually supports my claim!
Its true, and would also hold true for the GFCI itself. All the GFCIs I have seen have a fixed resistor, not a voltage compensated testing assembly. So the manufacturer has to intentionally select a lower value to compensate for installations that are within the lower bandwidth of voltage tolerances. This means that supplies at the higher level, like 126.5 volts will produce more current at time of testing.
So again, we have no real idea of what imbalance the GFCI sees under a test, often more to cover low voltage cases. However, a microprocessor testing device can pull the exact current desired with a display screen.
Yes, a short coming of not using a real tester like those deployed in the UK where parameters can be adjusted over a broad range.
And he doesn't know either with the self test mechanism. What value did the self test place?
Correct, if the EGC is open, but then this right here claims we shouldn't use those 3 light plug in testers either.
In any case its better to know the EGC is open.
Of course.
Supervisory circuit? If they mean the test resistor, the GFCI pictured has a 10K resistor, (12ma), and further, if the voltage is in the upper limit? Its over 9ma even for a 9ma sized resistor at 120 volts.
And this is where a tester comes in, checking both Live and neutral have opened. :thumbsup: And no, a 3 light tester wouldn't catch a hung up neutral.
But again, this is just comparing a tester vs an internal resistor. Still doesn't give much info on ma during testing, speed, or successful opening of all contacts.
A tester would tell me:
With an immediate imbalance drop;
Time to trip at 3ma, abort after 6 seconds (just to check for nuisance tripping)
Time to trip at 5ma (abort after 13 seconds)
Time at 10ma
Time at 15ma
Time at 30ma
Time at 50ma
Then we do a ramp test to determine the current rise in relation to the trip time.
Yes, that is about an external plug in tester which is not the same as the internal test.
There is no need to increase standards requirement when the existing ones are working fine. You have yet to post anything showing that existing standards are causing unsafe conditions.
There was a clear and easily provable need for seatbelts.
Sure with external testers.
If you actually read the text it explains that is not the case with the internal test button operation.
Above 126.5 volts is a problem in in itself. Do you think all electrical equipment needs to be designed to operate safely far above or below its nominal voltage rating?
So again you are looking for absolute safeguarding without showing any evidence it is needed,
Show me the injuries or property damaged caused by GFCIs failing to test properly operating out of their voltage range.
I agree those plug in testers are not a good way to go. Never said they were. I have been saying the internal tester does the job.
The standards tell us that the internal test is all we need.
Please show us how not knowing the precise value has caused injuries or deaths.
Do you understand that paragraph you are responding to is about external testers?
That document was written quite a while ago, the newer GFCIs do more supervisory.
http://www.legrand.us/passandseymou...t-gfci/ul-943-gfci-standard.aspx#.VXQrwVKgsrc
And that is just the latest up grade to the standards, there have been other upgrades since that OSHA document was published.
It is just not how things are typically done here. The standards and the codes do not require extensive testing. If testing and documentation is required, it is required by the contract documents and not a code or standard. It would be somewhat rare for the contract documents to require testing and documentation for dwelling units. That is much more commonly found on industrial and larger commercial projects, but not even on all of them.I?m giving up, I?m right in that everything should be tested and recorded and you?re right because there are more of you.
Testing costs money and if the contract documents don't require it, it won't happen.Now if someone comes up with a logical explanation of why things shouldn?t be tested other than MCB?s I?ll listen. ...
Our GFCIs are typically 15 and 20 amp devices with a few up to the 60 amp range....Regarding my statement about the RCD exploding, a 125A RCD is a bit unforgiving with an internal short circuit.
In an lot of areas in the US, there is no license required to do electrical work, and even in some places where a license is required, all you have to do to get the license is pay the fee.I?ve done very few domestic installs, it works out at about one every eight years. That is the reason I had another electrician test my flat. I?m authorised to work and test up to 11KV and yet I can?t test a domestic install.