hillbilly1
Senior Member
- Location
- North Georgia mountains
- Occupation
- Owner/electrical contractor
You may have a totally unrelated issue, is the ground from the uf cable terminated to anything at the source end? such as cold water, ground rod ect? If you are able to read voltage from earth to the box, turn off the breaker or remove the fuse feeding the receptacle. If the voltage goes away, the issue is with that installation, if it does not, Turn off other circuits in the panel one at a time until the voltage goes away. There is probally a high resistance fault to ground on one of the circuits, and the box may have a better ground than you think, and may be providing a return path for the fault.