Arc fault breaker

Status
Not open for further replies.

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
Replace it with a regular breaker. If it holds, you have a lose connection or possibly a flying splice.
An AFCI found a flying splice that I would have never found if I hadn't upgraded the breakers to AFCI's.
That's assuming someone didn't return a self test dualfunction when the self test indicated and issue. Best way to test would be the new gfci breaker and then a new afci after showing that the gfci is not detecting a ground fault. When afci trips its never instantaneous its after a second or 2 then they trip.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
The issue can not be anywhere upstream from the breaker.

Remove the Green bonding screw from the neutral buss bar at the sub panel.
I thought my comment. The green bonding screw is not at fault.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
The pigtail neutral is on the upstream side of the monitoring AFCI circuitry.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
The pigtail neutral is on the upstream side of the monitoring AFCI circuitry.
Yes

Sent from my SM-A025U using Tapatalk
Assuming circuit wiring is not connected to the breaker.
So, with the pigtail disconnected, when you connect the breaker to the buss bar and turn it ON, it stays ON, Correct?
As soon as the pigtail is connected to the neutral buss the breaker trips, correct?
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Just to go over this again. This sub-panel only has two breakers. Both are exactly the same AFCIs. Only one trips as soon as you apply power to the sub-panel. You changed the AFCI that trips to a new one. Now that breaker does the same thing.

Have you tried moving the breaker that trips to another position in the sub-panel?

-Hal
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
On the breaker, Have you checked continuity?
between
pigtail neutral and line side of the breaker
Pigtail and load side of the breaker
Load neutral and line side of....
Load neutral and load side of....
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
Let's try this.
 

Attachments

  • NATIONAL ELECTRIC CODE 2023 - Section 200.4(C) Proposed Amendment.pdf
    128.2 KB · Views: 19