Arc fault breaker
Replace it with a regular breaker. If it holds, you have a lose connection or possibly a flying splice.
An AFCI found a flying splice that I would have never found if I hadn't upgraded the breakers to AFCI's.
That's assuming someone didn't return a self test dualfunction when the self test indicated and issue. Best way to test would be the new gfci breaker and then a new afci after showing that the gfci is not detecting a ground fault. When afci trips its never instantaneous its after a second or 2 then they trip.
The issue can not be anywhere upstream from the breaker.
Remove the Green bonding screw from the neutral buss bar at the sub panel.
I thought my comment. The green bonding screw is not at fault.
The pigtail neutral is on the upstream side of the monitoring AFCI circuitry.
Yes
Sent from my SM-A025U using Tapatalk
Assuming circuit wiring is not connected to the breaker.
So, with the pigtail disconnected, when you connect the breaker to the buss bar and turn it ON, it stays ON, Correct?
As soon as the pigtail is connected to the neutral buss the breaker trips, correct?
Just to go over this again. This sub-panel only has two breakers. Both are exactly the same AFCIs. Only one trips as soon as you apply power to the sub-panel. You changed the AFCI that trips to a new one. Now that breaker does the same thing.
Have you tried moving the breaker that trips to another position in the sub-panel?
-Hal
On the breaker, Have you checked continuity?
between
pigtail neutral and line side of the breaker
Pigtail and load side of the breaker
Load neutral and line side of....
Load neutral and load side of....
Let's try this.