There are times a short circuit may "burn clear" without the OCPD actually opening.
Short Circuit: A fault between two conductors that cause a properly sized OCPD to open, which does not include the Equipment Grounding Conductor of a circuit.
IBEW441dc said:Short Circuit-An intentional or unintentional, low impedance conducting connection, between any ungrounded conductor(s) establishing a difference of potential, or between any ungrounded conductor(s) and a grounded conductor.
FPN (1): A Short circuit is not a Ground Fault (see Article 250.2 Definitions)
FPN (2): A Short Circuit is not an intentional or unintentional electrical conducting connection between a grounded conductor and an equipment grounding conductor.(see 250.6 Objectional Current)
The connection of an unintended Grounded Conductor to an EGC is Objectional Current. (see 250.6) Not a Short Circuit and not a Ground Fault.
I thought a connection between a grounded conductor and an EGC was a ground fault condition and the result of this connection was objectional current flow.
I do agree that there should be a clear definition for shrt circuit in Art. 100. I understand where you are comming from, take the term receptacle and outlet they are used interchangablly all the time in our industry.
Joe
Every wonder what the definition of a SHORT CIRCUIT was in the NEC?(I sure do)
Article 100-Part I and II should include an authoritative definition of the commonly used (and easily mis-used term).
Okay.....to avoid this part........I know, I know....see 90.1(C).blah, blah , blah...a trained person should know what a short circuit is.True, but based on what reference?, I challenge you to google it, check different dictionary's, IEEE, maybe NEMA even? My point is .....the different sources imply different things.
......A trained person should respect the fact that we all have to be accountable to an authority.........in the 'Electrical Installation World', that authority is NFPA 70(NEC).
The NEC states pretty clearly what an Overcurrent is and subdivides it into 3 categories.:smileand this is only one example)
Overload is in Article 100, Ground Fault is in 250,..... so where is SHORT CIRCUIT?
1 : to apply a short circuit to or establish a short circuit in
2 : bypass
3 : frustrate , impede
Short Circuit = ungrounded to ungrounded = fault current
Ground Fault = ungrounded to EGC = fault current
? = grounded to EGC = objectionable current
Joe
the first one is close....
Short Circuit= ungrounded to ungrounded, and ungrounded to grounded(neutral)=Fault Current
Ground Fault=ungrounded to EGC=Fault Currrent.....Bingo!:smile:
Objectional Current = grounded to EGC=Objectionable Current......correct-a-mundo:smile:
Assuming a systems neutral conductor is properly bonded at the service to the EGC,via the MBJ, the voltage potential is zero (between the two). From that single point all the way to the final load, the neutral and EGC must be kept independent of each other(the voltage between the 2 is still zero).A neutral to EGC bond that establishes parallel path for neutral current will not create an explosion like a fault (short circuit or a ground fault)because there is no difference of potential. But what does happen is you have neutral current flowing on metal parts not intended to perform that function, Objectionable Current, not fault current.
A neutral to case bond at other than the Service, and a neutral to case bond at other than the source of a separately derived system are examples of establishing objectionable current.
I understand what you are saying , I'm just having a difficult time with the terms. It seems redundant to me to label the condition and the result with same term. The result of a ground fault or a short circuit condition is fault current but the result of objectionable current is objectionable current.
Joe
Do we need to define it?
Is the term 'short circuit' currently being used in the NEC and causing people confusion or misinterpretation of the NEC?
Yes, I do think a definition would be a valuable addition to the NEC.
I think the lack of this definition does create confusion or misinterpretation of the NEC.
A similar example of 'definition evolution' is pretty much everything associated with Grounding and Bonding.Don't you agree that prior to the recent changes,especially in the 08 NEC, the lack of proper definitions created confusion or misinterpretation.
Now before you say....that's a different issue all together, consider the fact that Short Circuit is commonly misused to describe a ground fault or objectionable current.
Humoring your idea for a moment (which I still disagree with), is there a safety concern here?Yes, I do think a definition would be a valuable addition to the NEC.
I think the lack of this definition does create confusion or misinterpretation of the NEC.
Absolutely, and there was a genuine safety impediment with the confusion of the terms. There's no requirement to create a short circuit (okay, maybe one I can recall). There are multiple requirements to create "grounds".A similar example of 'definition evolution' is pretty much everything associated with Grounding and Bonding.Don't you agree that prior to the recent changes,especially in the 08 NEC, the lack of proper definitions created confusion or misinterpretation.
This statement is not correct assuming that any current is on the circuit and it is properly bonded at only one point.Assuming a systems neutral conductor is properly bonded at the service to the EGC,via the MBJ, the voltage potential is zero (between the two). From that single point all the way to the final load, the neutral and EGC must be kept independent of each other(the voltage between the 2 is still zero)..
Ground fault and objectional current are covered in the NEC and much documetation.
Adding a definition is not going to stop the confusion. People reading and studying is going to help.
This is a very confusing part of the code partly because some of the teachers who teach us basic ohms law simplify it without calculus so that the average joe shmoe can grasp it quickly enough for basic electrical work.Adding a definition is not going to stop the confusion???:-?I don't even know how to respond to that. A definition would IMO be an attempt.
People reading and studying is going to help, although those who do so will be held accountable for the things we say and do. Clearly defining terms in an appropriate manner is extremely important.
Humoring your idea for a moment (which I still disagree with), is there a safety concern here?
Absolutely, and there was a genuine safety impediment with the confusion of the terms. There's no requirement to create a short circuit (okay, maybe one I can recall). There are multiple requirements to create "grounds".
Not knowing what they're talking about when creating a grounding system can result in a fatality. Is there a similar problem with the term "short circuit"?
Hmmmm????the effects of short circuits or ground faults must be dangerous.....Article 250 defines a ground fault......so I clearly know what to avoid there. But what is a short circuit.....it sounds dangerous too(as a matter of fact more dangerous)90.8(B) Number of Circuits in Enclosures. It is elsewhere provided in this Code that the number of wires and circuits confined in a single enclosure be varyingly restricted. Limiting the number of circuits in a single enclosure minimizes the effects from a short circuit or ground fault in one circuit.
A short circuit is a hazard arising from the use of electricity.90.1 Purpose.
(A) Practical Safeguarding. The purpose of this Code is the practical safeguarding of persons and property from hazards arising from the use of electricity.
A definition of Short Circuit would clear up any debate as to its meaning to trained persons, thus resulting in safer installations.(C) Intention. This Code is not intended as a design specification or an instruction manual for untrained persons.
I press this because you are going to be pressed by the CMP for a very good answer to that question. I can already hear the statement "the existing language has been used successfully for many years. Insufficient substantiation to add a definition."
This statement is not correct assuming that any current is on the circuit and it is properly bonded at only one point.
The resistance of the wire is in series with the load and causes a proportional voltage drop on both sides of the load which is determined by the resistance of the wire and the voltage of the source.
Assuming the wire length and mechanically connected parts are eaqually conductive. There is a potential difference always between a conducting cable and a non conducting cable of the same length/resistance.
This of course gets more complicated when we are talking 3 phase loads.
When the conducting grounded cable comes into contact with ground at the load the resitance of the 2 cables is halved ( This model also ignores all current actually carried by dirt-earth) and the total circuit current rises slightly yet the current is split on the 2 wires back to the source to the point of service bonding.
This is a fairly complex mathematical process which is oversimplified for most teaching purposes. This must also include capacitive and inductive coupling along the route and the changes in reactance and suseptance when a neutral is grounded to the ground wire at the load.
If you dont believe this touch the neutral to ground at a load and then explain why the gfci tripped.
I totally agree that this definition is horrible and the Nfpa really dropped the ball with all of these engineers running around there and no one picked up on this. To define a ground fault as only on ungrounded conductors is simply dangerous and wrong in my opinion.
Heck what do I know I am just a dumb electrician???
This is a very confusing part of the code partly because some of the teachers who teach us basic ohms law simplify it without calculus so that the average joe shmoe can grasp it quickly enough for basic electrical work.
As you get more into the calculus it opens up a whole can of worms with many different things going on simultaneously and not to be ignored.
For example when you study a lightbulb being powered the current on the copper is studied and the current on the air we breath and the current on the wire insulation is ignored because thier values are so low that they can be thrown out.
Enter an arc flash where the air becomes Ionized and we have a whole different animal. Draw that using ohms law acurately you will be busy for a while.
ALL paths must be counted in the equation for the engineers version. Simplified one line diagrams for the rest of us
Yes, I do think a definition would be a valuable addition to the NEC.
I think the lack of this definition does create confusion or misinterpretation of the NEC.
A similar example of 'definition evolution' is pretty much everything associated with Grounding and Bonding.Don't you agree that prior to the recent changes,especially in the 08 NEC, the lack of proper definitions created confusion or misinterpretation.
Now before you say....that's a different issue all together, consider the fact that Short Circuit is commonly misused to describe a ground fault or objectionable current.
Give us an example of where the NEC uses the term short circuit that leads to confusion.
90.8(B) Number of Circuits in Enclosures. It is elsewhere provided in this Code that the number of wires and circuits confined in a single enclosure be varyingly restricted. Limiting the number of circuits in a single enclosure minimizes the effects from a short circuit or ground fault in one circuit.
NECPLUS-Staff Note for 90.8(B)
The limitations noted in 90.8(B) on number of wires and circuits in a single enclosure also minimize the heating effects inherently present whenever current-carrying conductors are grouped together.