ibew441dc
Senior Member
The last incarnation of your proposal still stated that a short was only between two ungrounded conductors, I believe, which I still disagree with. If you were to create a definition and try to sell it to the CMP, then I would say:
Short Circuit: An intentional or unintentional low-impedance connection between two insulated conductors.
I would say anything wrong other than that is a ground fault.
My last incarnation did not limit a short as being between 2 ungrounded conductors.......go back and look.
Originally Posted by IBEW441DC
Short Circuit-An intentional or unintentional, low impedance conducting connection, between any ungrounded conductor(s) establishing a difference of potential, or between any ungrounded conductor(s) and a grounded conductor,or between any ungrounded conductor(s) and an equipment grounding conductor.
FPN (1): A Ground Fault is not a short circuit when subject to high impedance (see Article 250.2 Definitions).
FPN (2): An Arc Fault is not a short circuit due to high impedance.
FPN (3): A Short Circuit is not an intentional or unintentional electrical conducting connection between a grounded conductor and an equipment grounding conductor.(see 250.6 Objectionable Current) An example of objectionable current is neutral current flowing on paths other than permitted by the Code.
As far as your comments to the other rules where the terms short circuit and ground fault are equal.....I still firmly disagree. A Ground Fault by definition is a defined path. A Short Circuit by accepted definition has low impedance. A Ground Fault may or may not have low impedance, where a short circuit always does. Following the same logic, an Arc Fault is not a short circuit due to high impedance.