IMO the key difference is the impedance. A Short Circuit has low impedance. A ground fault is not a Short Circuit when subject to high impedance. An Arc Fault is not a Short Circuit due to high impedance. A "Bolted Fault" line to line,line to neutral, or line to EGC is a Short Circuit due to low impedance. By the way where did you come up with "Bolted Fault" :grin:?
The NEC addresses these faults based on their path.
Overcurrents - excess current flowing through the entire intended circuit conductors including the load.
Short Circuits - current flowing along portions (i.e. not through the load)of the intended circuit conductors.
Ground Faults - current flowing outside of the intended circuit conductors.
You appear to want the NEC to define these faults based on the voltage drop across the 'fault' (i.e. its impedance). However, the amount of impedance in a fault (arcing, bolted, or excessive loading) is not always path related.