(1)What is a Short Circuit?
(2)What is a Ground Fault?
(3)What is Objectionable Current?
(4)What is an Arc Fault?
(5)Is a Ground Fault a Short Circuit?
(6)Is a Short Circuit a Ground Fault?
(7)Is an Arc Fault a Short Circuit?
Short Circuit; A circuit of short length, example; A dedicated circuit to a receptacle underneath a panel board connected with a chase nipple.
Problem solved. :wink:
Roger
Obviously:roll::smile:, My opinion is now biased in this regard, and so is yours. How do we come to a conclusion if both are convinced that either (a) the definition would provide clarity and be beneficial ,or (b) the definition is unnecessary and would be of no benefit
(3)What is Objectionable Current?
No one knows.
The NEC is not a design manual or instructions for the untrained. The stated purpose of the NEC is providing safe electrical installations
I am asking a straight forward question that you can't seem to answer.
How would adding a definition of 'short circuit' into Article 100 increase electrical safety?
Keep in mind these are the types of questions the CMP will be thinking about.
I think that a ground fault definition should be any conductor other than a ground that has faulted to ground. How was that for starters?IWIRE, you have not asked me such a question until now. (paraphrasing)You asked me where in the code it may cause confusion, and I have answered that.
Adding the definition of 'short circuit' would increase electrical safety by identifying language as to avoid dialog confusion of a commonly used term among qualified persons, clearly illustrating the portion of a circuit that has the highest fault current available at that point.
Short Circuit; A circuit of short length, example; A dedicated circuit to a receptacle underneath a panel board connected with a chase nipple.
Problem solved. :wink:
Roger
You're ignoring the fact that a short circuit could include an ungrounded and grounded conductor making contact after the service disconnect.Adding the definition of 'short circuit' would increase electrical safety by identifying language as to avoid dialog confusion of a commonly used term among qualified persons, clearly illustrating the portion of a circuit that has the highest fault current available at that point.
You're ignoring the fact that a short circuit could include an ungrounded and grounded conductor making contact after the service disconnect.
Is there a lesser level of PPE I must wear if I'm only going to be exposed to a ground fault? I must have missed the memo...?
Originally Posted by IBEW441DC
Short Circuit-An intentional or unintentional, low impedance conducting connection, between any ungrounded conductor(s) establishing a difference of potential, or between any ungrounded conductor(s) and a grounded conductor,or between any ungrounded conductor(s) and an equipment grounding conductor.
FPN (1): A Ground Fault is not a short circuit when subject to high impedance (see Article 250.2 Definitions).
FPN (2): An Arc Fault is not a short circuit due to high impedance.
FPN (3): A Short Circuit is not an intentional or unintentional electrical conducting connection between a grounded conductor and an equipment grounding conductor.(see 250.6 Objectionable Current) An example of objectionable current is neutral current flowing on paths other than permitted by the Code.
I don't understand - why do you say the fault current would be higher from ungrounded to grounded than ungrounded to grounding?My logic still applies to an ungrounded and grounded conductor because if they were the only conductors together the fault current would be higher than an ungrounded to EGC fault(ground fault).
My logic still applies to an ungrounded and grounded conductor because if they were the only conductors together the fault current would be higher than an ungrounded to EGC fault(ground fault).
I don't see any confusion in the application of the code now and see no need for a definition of short circuit.
As far as the neutral conductor, that was an undefined term in the NEC, but it took at least 3 code cycles to arrive at a workable definition.
I don't understand - why do you say the fault current would be higher from ungrounded to grounded than ungrounded to grounding?
My logic still applies to an ungrounded and grounded conductor because if they were the only conductors together the fault current would be higher than an ungrounded to EGC fault(ground fault).
Almost more than the voltage, the impedance in the fault path dictates the amount of current that flows during a fault. All other things being equal, the highest amount of current occurs during a bolted fault condition and the lowest during an arcing fault. It is possible to have a bolted ground fault with a 'high current' value and an arcing short circuit fault with a 'low current'.
I suggest that a short circuit is simply a fault path that bypasses the intended load.
I could see where there was a code application or use impact with the term neutral...I just don't see that for "short circuit"."Neutral" was defined for many years in the same manner that "Short Circuit" is defined now. It was assumed to be understood using outside references. For the sake of argument, forget my interpretation of Short Circuit, even if the NFPA would include a definition of their choosing in the Code, it would be appropriate.
I could see where there was a code application or use impact with the term neutral...I just don't see that for "short circuit".