I have read the entire thread. There seems to be more than a few things being discussed. I still don't understand why you responded to don that way, but thats ok. This question was asked of Mike Holt; this was his response and I agree with it.
Is AFCI protection required for switches located in the bedroom that controls a lighting outlet in another space?
If the switch controls utilization equipment in the bedroom, then it will be AFCI protected. However, if the switch operates lighting outlets for outdoor luminaire, closets or other loads not terminated in bedroom space then AFCI protection is not NEC required, because a switch is not considered an outlet*.
*According to Article 100, an outlet is defined as a point on the wiring system at which current is taken to supply equipment that utilizes electric energy for electronic, electromechanical, chemical, heating, lighting, or similar purposes [100]. This would include a receptacle outlet, a lighting outlet, but not a switch.