Re: Big oops ... need suggestions
Originally posted by iwire:
An outlet supplies utilization equipment, a switch supplies premises wiring.
Bob, forgive me for coming back to this again, but it has been rattling around in my head all morning. The crux of the confusion lies in "a switch
supplies premises wiring."
And my point speaks directly to your last post, Charlie B.
A switch cannot supply premises wiring. Current does not enter the premises wiring from a switch and then return to the switch. Rather current enters the switch and returns to the premises wiring.
That is identical to a receptacle outlet current going out of the premises wiring to the utilization equipment and returning to the premises wiring. Never mind voltage. . .voltage is not in the definition. . .the definition of Outlet only looks at current.
Outlet is such an old, old, old and unchanged definition, I think we have become too sophisticated to appreciate its simplicity.
An Outlet is not an inlet, if you will allow me to use the term. I mean, current at the point of an inlet enters and returns from the Premises Wiring (System). This is the Service Point when a poco is involved.
An outlet is the point where current comes out and returns to the Premises Wiring (Sytem).
Current let in vs. current let out. That simple.
Edit typos & ran spell check - Al
[ October 18, 2005, 11:52 AM: Message edited by: al hildenbrand ]