Can someone please explain this to me?

Status
Not open for further replies.

steve66

Senior Member
Location
Illinois
Occupation
Engineer
I have reservations about using that OLC.

And since this is a practice problem, I really wouldn't expect someone to use an online calculator to get the answer.

Maybe to check the answer, but when we don't get the right answer, its pretty obvious this calculator makes assumptions (like the Power Factor) that aren't part of the original problem.
 
Daniel, I don't want to get into a pissing contest on this, but most breakers today (rated under 100A) are rated for both 60c and 75c terminations. I agree that other terminations need to be considered. Circuits less than 40-amps will rarely ever be used at ampacities that require a 75c termination, just the way it is. But ... it is not true that a circuit under 100A has to be calculated at the 60c termination because of the circuit breaker because most of them are also rated for 75c terminations (other current limiting terminations may be in the circuit but it's not usually the circuit breaker that needs to be considered).
I just looked on several breakers GE 40°, Sq D home line 40°, Sq D QO 40°, Siemens 40°, Cutler Hammer Ch 60-75° Cutler Hammer bolt in 60-75° most are 40°. I got no reason to lie to ya.

Sent from my SM-T350 using Tapatalk
 

Carultch

Senior Member
Location
Massachusetts
I just looked on several breakers GE 40°, Sq D home line 40°, Sq D QO 40°, Siemens 40°, Cutler Hammer Ch 60-75° Cutler Hammer bolt in 60-75° most are 40°. I got no reason to lie to ya.

Sent from my SM-T350 using Tapatalk

I think that is the ambient temperature, not the termination temperature.
 

oldsparky52

Senior Member
I just looked on several breakers GE 40°, Sq D home line 40°, Sq D QO 40°, Siemens 40°, Cutler Hammer Ch 60-75° Cutler Hammer bolt in 60-75° most are 40°. I got no reason to lie to ya.

Sent from my SM-T350 using Tapatalk

Well since you must have at least a 60c connection, all of the breakers you listed may not be used ... but ... since we use them, .... maybe, just maybe you are misunderstanding some of the information you are presenting?

Most likely the 40c ratings are the ambient temperature ratings, and the 60c-75c ratings are the termination ratings. Two completely different items. One is for the air around the breaker and the other directs us as to what ampacity table we are allowed to use.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
I don't really have a handle on how PF effects VD, can you help me with that? I understand why and how it affects KW (as compared to KVA), but not VD.

Thanks.

Actually, I think the Southwire calculator assumes 3 phase. That makes a bigger difference than the power factor. I don't seen anywhere on the Southwire calculator where I can choose 1 phase.

But back to the power factor - it makes some difference in the calculated impedance of the wire. If you know R and X for a wire, then Z depends on R and X and the power factor.

Z = X*PF+R*Sin(Acos(PF))

(I think that's right - I'm trying to read it from an excel formula.)

Just as an example, my Square D calculator lists L-L voltage drop per amp per 100' in magnetic copper wire: (trying to make a table, which isn't working)

....................... ..... #8 Wire #10 wire
1 phase: 90% PF. . 0 .15 ....... . 0 .23
1 phase: 80% PF ...0.13 ........ 0 .20
3 phase: 90% PF .. 0 .13 ........ 0 .20
3 phase: 80% PF... 0 .11 ........ 0 .17
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
That was ambient temperature, not termination rating.



On page 7 you will find
Correct, the ambient is marked on the breaker, the terminal rating may or may not be found on the breaker or the terminals, but it can always be found in the manufactures tech sheets.

I think that is the ambient temperature, not the termination temperature.
Correct again.

Well since you must have at least a 60c connection, all of the breakers you listed may not be used ... but ... since we use them, .... maybe, just maybe you are misunderstanding some of the information you are presenting?
I think he has hit the nail on the head Daniel

Most likely the 40c ratings are the ambient temperature ratings, and the 60c-75c ratings are the termination ratings. Two completely different items. One is for the air around the breaker and the other directs us as to what ampacity table we are allowed to use.
:thumbsup:

Roger
 
I looked again at breakers. You are right i do see terminal ratings below the 40° marking and they are all 60° -75° C rated terminals. What does the 40° C ambient marking mean?

Sent from my SM-T350 using Tapatalk
 

Fnewman

Senior Member
Location
Dublin, GA
Occupation
Sr. Electrical Engineering Manager at Larson Engineering
In my mind, way too much discussion for what is really a simple, possibly trick question. If it is a 30 amp load, given no other information, you have to assume continuous. That equals a #8 circuit and calculator.net gives a drop of 1.64%. The calculator instructions specifically state NOT to use round trip distance.
 

oldsparky52

Senior Member
Actually, I think the Southwire calculator assumes 3 phase. That makes a bigger difference than the power factor. I don't seen anywhere on the Southwire calculator where I can choose 1 phase.

But back to the power factor - it makes some difference in the calculated impedance of the wire. If you know R and X for a wire, then Z depends on R and X and the power factor.

Z = X*PF+R*Sin(Acos(PF))

(I think that's right - I'm trying to read it from an excel formula.)

Just as an example, my Square D calculator lists L-L voltage drop per amp per 100' in magnetic copper wire: (trying to make a table, which isn't working)

....................... ..... #8 Wire #10 wire
1 phase: 90% PF. . 0 .15 ....... . 0 .23
1 phase: 80% PF ...0.13 ........ 0 .20
3 phase: 90% PF .. 0 .13 ........ 0 .20
3 phase: 80% PF... 0 .11 ........ 0 .17

So, ... as PF goes farther away from 1, the resistance in the circuit becomes less? So the worse the PF the less resistance?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Actually, I think the Southwire calculator assumes 3 phase. That makes a bigger difference than the power factor. I don't seen anywhere on the Southwire calculator where I can choose 1 phase.

My Southwire app has a place to choose single ø or 3 ø.
 