That’s why everyone shames the NEC because thered certain rules to follow sometimes not always and those rules only apply to some things not all things.
You did not read nec 110.14c1That's not how it is worded in the Code at all.
The Code says... Ampacities for conductors rated 0 volts to 2000 volts shall be as specified in the Ampacity Table 310.16 through Table 310.21, as modified by 310.15(A) through (F) and 310.12.
There's no wording in the Code about the other ampacity tables being used to start with a higher ampacity but reduced to table 310.16.
It
It is and i even submited the necs explanation as to why. See pictute of nec text
I did in fact read NEC 110.14(C)(1). It doesn't say anything about the other ampacity tables being used to start with a higher ampacity but reduced to table 310.16.You did not read nec 110.14c1
Very good point . If it’s one of the specific applications listed in 240.4(g) it’s not subject to the restrictions of 240.4(d)(1-8)See NEC 240.4(D) and what follows. There is a difference between a wire's nominal ampacity and what OCP may be used to protect it under various circumstances.
You did not read nec 110.14c1
You did not read nec 110.14c1
No, not "for any reason," only for "termination provisions".Meaning only time l amapcity values from another table can be used for any reason is if the equipment is specifically listed and Marked for that use . Which means its dictated by the equipment not the wiring method
No, not "for any reason," only for "termination provisions".
For an example, say I have a branch circuit that needs to supply some equipment within a wood-drying kiln where part of the run is exposed to 90C ambient. Obviously I can't use 90C conductors, but I could use Type Z conductors rated at 150C per Table 310.4(A) footnote 3. Type Z conductors in conduit can use Table 310.18 for their ampacity. But at the panel supplying the branch circuit, per 110.14(C) I would need to use Table 310.16 for the termination ampacity.
Cheers, Wayne
And on that note the a conductors termination ampacity is dictated by the terminal temp rating of the equipment, ie: equipment provisions . Correct ?No, not "for any reason," only for "termination provisions".
For an example, say I have a branch circuit that needs to supply some equipment within a wood-drying kiln where part of the run is exposed to 90C ambient. Obviously I can't use 90C conductors, but I could use Type Z conductors rated at 150C per Table 310.4(A) footnote 3. Type Z conductors in conduit can use Table 310.18 for their ampacity. But at the panel supplying the branch circuit, per 110.14(C) I would need to use Table 310.16 for the termination ampacity.
Cheers, Wayne
Whats interesting is how 110.14(C)(1) states in part;Why would it depend on the conductor size connected to it? If the termination can carry 200A without exceeding it's 75deg rating,, then the rating is 200A.
Unless the equipment is listed and marked otherwise,
conductor ampacities used in determining equipment termination
provisions shall be based on Table 310.16 as appropriately
modified by 310.12
Obviously no, as the sentence you quoted says to use Table 310.16 "unless the equipment is listed and marked otherwise." So unmarked = use Table 310.16. But as the equipment manufacturer, you could choose to have it so listed and marked, so that the installer has the option to use #2 Cu when the equipment is installed with unenclosed terminations.Now if my equipment with that same lug can be used in free air (per the definition) could that lug
still handle 150A from a #2 CU (Based on 310.17) without me needing to mark the equipment otherwise?
Obviously no, as the sentence you quoted says to use Table 310.16 "unless the equipment is listed and marked otherwise." So unmarked = use Table 310.16.
It includes the conductor size terminated on the equipment, and the ampacity we associate to that combination. It does not cover anything about determining the ampacity of a circuit conductor at a location outside the equipment.Nothing is obvious to me you should know that by now.
110.14(C)(1) is saying to use 310.16 or 310.12 in determining equipment termination
provisions , so do you think 'equipment termination provisions ' includes the branch circuit conductor?
It if sounds to me like he thinks 110.14(c)(1) is saying we can use ampacity values from other tables as a starting point when applying any required ampacity correction adjustment factors (derate) Which to me makes no sense since the ampacity of a conductor at its termination point can only come from table 310.16 unless the equipment is specifically listed and marked saying otherwiseI did in fact read NEC 110.14(C)(1). It doesn't say anything about the other ampacity tables being used to start with a higher ampacity but reduced to table 310.16.
Are you sure thats how UL 486A-B does it?It includes the conductor size terminated on the equipment, and the ampacity we associate to that combination.
No you don't.Can somebody stop reciting every code article and just make a very simple response? You size your wire based on the over current protection device.
There are ambient temperature correction factors, number of conductors in a conduit, termination temperature ratings, free air allowances, manufacture specs, and some more I can't think of.There’s no need to get into the wires ampacity capability in 100 different situations.
Most of the time that works, but not all the time.I have never looked at a piece of equipment and seen the amp rating but the looked at the lug rating to determine the wire amp rating to use. Quit over killing it if it’s 20a use #12 if it’s 30a use #10 if it’s 40a use #8 ect..