pierre
Senior Member
- Location
- Westchester County, New York
Re: Dedicated Circuit for referigerator
I was going to stay out of this, but... I just can't
I have been reading back and forth and have to agree to the casual reader of the NEC it would seem this is like a heavy weight fight, where each fighter has thrown a punch that could seem like the knockout punch.
Without knowing exactly what the CMP was thinking here, the wording is tough to interpret, so we have to look hard for an answer (without a formal interpretation). Maybe this will help.
220.52(A) Exception: The individual branch circuit permitted by 210.52(B)(1), Exception No. 2, shall be permitted to be excluded from the calculation required by 220.52.
IMO - this would support the side that believes the first 2 small app branch ckt are used in the calculations, and that the rest are not required to be, but could be if so desired.
I was going to stay out of this, but... I just can't
I have been reading back and forth and have to agree to the casual reader of the NEC it would seem this is like a heavy weight fight, where each fighter has thrown a punch that could seem like the knockout punch.
Without knowing exactly what the CMP was thinking here, the wording is tough to interpret, so we have to look hard for an answer (without a formal interpretation). Maybe this will help.
220.52(A) Exception: The individual branch circuit permitted by 210.52(B)(1), Exception No. 2, shall be permitted to be excluded from the calculation required by 220.52.
IMO - this would support the side that believes the first 2 small app branch ckt are used in the calculations, and that the rest are not required to be, but could be if so desired.