Re: Dedicated Circuit for referigerator
No Bob it does not mean that we are required to install two and more at the same time. The meaning is clear if you will set your feelings aside and read it with an open mind.
Forget the thought that only two are required. The section does not say this. It clearly states two or more.
It mandates that no less than two but if more are installed they will carry the same weight as the first two.
This locks them into the calculation of the service as outlined in 220.52 (A) and 220.82 (B) (2).
Unlike the general lighting of a dwelling unit where we use the three watt per square foot rule and are allowed to have as many overcurrent devices as we want to comply. The small appliance circuits have a stricter set of rules.
In the class room I use the optional load calculation as outlined in 220.82 to show how the NEC lays weight on the circuits of a dwelling unit. First comes the general lighting then the small appliance and laundry, third we find the larger appliances such as ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and water heaters that are to be on specific circuits. Then comes the motors. Last we find the heat and air conditioning which is the largest of the loads.
We find that as the circuits are outlined they become more restrictive by nature. This is also how they are outlined in the articles of the code book.
Like it or not this is what the code mandates as it applies to the small appliance circuits. Weather you want to admit it here doesn?t matter to me at all. What do matter are those that do not know being swayed in the wrong direction.
You keep making the statement that this is MY view as though you think I just made this up. This also is far from the truth. Several have posted their findings in text books as well as the insert from the handbook that states the same thing. No this is not something that I thought up it is something that I have learned from others.
The bottom line to 210.11 (C)(1) is a mandatory rule and there is no permission given nor implied. If you have 20 receptacles on 20 circuits then they calculate at 20 times 1500 VA.