Re: Dedicated Circuit for referigerator
I agree with you Don
I don?t understand why there is this debate when 210.11 (C)(1) clearly states the words two or more.
Would this not mean that when I reference 210.11 (C)(1) I would reference the section as a whole instead of just part of it?
I clearly see the word ?more? so if ?more? is there then would not ?more? be included?
What I don?t see in 210.11 (C)(1) are the words ?shall be permitted?
210.11 Branch Circuits Required, (C) Dwelling Units, (1) Small-Appliance Branch Circuits, In addition to the number of branch circuits required by other parts of this section, two or more 20-ampere small-appliance branch circuits shall be provided for all receptacle outlets specified by 210.52(B).
This reads that if there are more than two circuits installed here then when we reference the section all that have been installed are to be included.
It does not say, In addition to the number of branch circuits required by other parts of this section, two required or more shall be permitted 20-ampere small-appliance
To read 220.52 (A) the way that has been proposed by some here would be to omit the word MORE from 210.11 (C) (1).
It does not say In each dwelling unit, the load shall be calculated at 1500 volt-amperes for two required 2-wire small-appliance branch circuit, but none for the 2 wire circuits that are permitted by 210.11(C)(1)
Instead it reads:
220.52 Small Appliance and Laundry Loads ? Dwelling Unit.
(A) Small Appliance Circuit Load. In each dwelling unit, the load shall be calculated at 1500 volt-amperes for each 2-wire small-appliance branch circuit required by 210.11(C)(1)
Being that CMP 2 included the words ?two or more? means that if there is more then these other small appliance circuits must be included. 210.11 (C)(1) is not a permissive rule as defined in 90.4
edited to put code in quotes
[ June 26, 2005, 09:51 PM: Message edited by: jwelectric ]