curt swartz
- San Jose, CA
- Electrical Contractor
We recently wired an addition to a single family dwelling and the owner wanted several exterior outlets installed for possible future lights in addition to the required outlets. We installed fixtures at required outlet locations (at exterior doors) but installed weatherproof blank covers on the other outlets. A final inspection was called by the homeowner last week and I was notified that the inspector would not accept blank covers and fixtures must be installed at all location. I figured that must have been a misunderstanding so I called the inspector the next morning. Below is a recap of our conversation. Let me know what you think.
Me: Hello inspector. I want to find out what you are requiring for the exterior light boxes at this project
Inspector: If a light box is installed a fixture must be installed and working for final inspection.
Me: These outlets are for possible future lights. They are not required outlets. Light fixtures are installed at the exterior doors. The wires in these boxes are insulated with wire nuts and a listed wet location blank cover is installed.
Inspector: Show me in the code book that you are allowed to install lighting outlets but not install the fixtures.
Me: I can?t
Me: What is the difference between these outlets and installing a circuit and disconnect for possible future central A/C?
Inspector: If a circuit for A/C is installed during rough the A/C unit must be installed for final. If you don?t install the A/C unit the wiring must be removed.
Me: You got to be kidding me! You are telling me that if I don?t install these fixtures I must remove the wiring?
Inspector: Yes, unless you can show me in the code book that you are allowed to install lighting outlets but not install the fixtures.
Me: Fine, these are not lighting outlets, they are junction boxes.
Inspector: Why are they installed?
Me: Because I wanted to.
Inspector: Since these are round lighting boxes you must install fixtures on them.
Me: So there is no legal use for blank covers?
Inspector: Not if there are wires behind them.
End
Me: I can?t
End