You mean the main breaker does not stop the fed from utility? I thought main breaker would allow one way fed from solar to grid.
Also more of the 705.12(D) quote....
"...where this distribution equipment is capable of supplying mulitple branch circuits or feeders or both......"
So where are the branch circuits or feeders in the 200A panelboard? I have none. So how can it apply?
Sent from my SM-G935U using Tapatalk
No you're going down a wrong road here.
First, it says 'capable of', not actually supplying.
Second, the circuits to the aggregators are feeders, and you have a branch circuit for the Envoy.
These definitions don't stop applying because they're connected to sources instead of loads.