I read solarpro article calculated worst case with 1.25 multiply but I got worst case 199.18A line current excluding Envoy which is still less than 200A. Am I missing something?
I thought it would be close but that's even closer than I thought it would be.
But now if you apply the vector calculation to the overcurrent devices which are referenced in 705.12(D)(2)(3)(c) - this was Wayne's suggestion - you come out over 200A. It's the 208A Wayne calculated back in post #24.