wac= washington (state) administrative (electrical) code:
"Flood Areas
WAC 296-46B-110(2) Electrical equipment and wiring that has been submerged or exposed to water must comply with the following:
(a) All breakers, fuses, controllers, receptacles, lighting switches/dimmers, electric heaters, and any sealed device/equipment (e.g., relays, contractors, etc.) must be replaced.
(b) All other electrical equipment (e.g., wiring, breaker panel boards, disconnect switches, switchgear, motor control centers, boiler controls, HVAC/R equipment, electric motors, transformers, appliances, water heaters, and similar appliances) must be replaced or reconditioned by the original manufacturer, or by its approved representative.
If exposed to flooding, an inspection must be made for: Any underground wiring, if any electrical connection was flooded, Any electrical equipment installed outdoors (e.g. mobile home pedestal, transformers, switches, receptacles, etc.), if any part of the equipment was flooded, Any structure with a basement area, Any structure where the maximum flood level reached the lower limit of the lower floor joists, or Any structure with a floor on grade."
just fyi. might help somebody in NJ or NY tho it certainly doesnot apply outside of wa
"Flood Areas
WAC 296-46B-110(2) Electrical equipment and wiring that has been submerged or exposed to water must comply with the following:
(a) All breakers, fuses, controllers, receptacles, lighting switches/dimmers, electric heaters, and any sealed device/equipment (e.g., relays, contractors, etc.) must be replaced.
(b) All other electrical equipment (e.g., wiring, breaker panel boards, disconnect switches, switchgear, motor control centers, boiler controls, HVAC/R equipment, electric motors, transformers, appliances, water heaters, and similar appliances) must be replaced or reconditioned by the original manufacturer, or by its approved representative.
If exposed to flooding, an inspection must be made for: Any underground wiring, if any electrical connection was flooded, Any electrical equipment installed outdoors (e.g. mobile home pedestal, transformers, switches, receptacles, etc.), if any part of the equipment was flooded, Any structure with a basement area, Any structure where the maximum flood level reached the lower limit of the lower floor joists, or Any structure with a floor on grade."
just fyi. might help somebody in NJ or NY tho it certainly doesnot apply outside of wa